Discuss High resistance on ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
25
I was to asked to add a spur on a ring circuit.
I done a continuity test to make sure i had a ring the N-N was 0.46 CPC-CPC was 1.08, But my L-L was 2.4, i went round every socket looking for a loose conection.
Tightened up a few loose sockets and the reading came down to 1.9 i coudlnt find any junction boxes as the house has recently been renovated with hardwood flooring throughout so i cant get access under floor or in a cupboard that has been closed off to check. Im not to happy leaving it as is but im at a bit of a dead end as to what i can do next. Any opinioms would be appreciated. Thanks
 
Last edited:
I was to asked to add a spur on a ring circuit.
I done a continuity test to make sure i had a ring the N-N was 0.46 CPC-CPC was 1.08, But my L-L was 2.04, i went round every socket looking for a loose conection.
Tightened up a few loose sockets and the reading came down to 1.9 i coudlnt find any junction boxes as the house has recently been renovated with hardwood flooring throughout so i cant get access under floor or in a cupboard that has been closed off to check. Im not to happy leaving it as is but im at a bit of a dead end as to what i can do next. Any opinioms would be appreciated. Thanks

Did you check for trapped insulation, conductors only just making contact in terminals?

If you have then it's probably a JB. split the ring in half at a socket, do a continuity test between leg at the board and leg at the socket using a wondering lead and repeat the process until you find it.
 
Thanks for the quick reply. Yes i checked for trapped insulation. My thinking is junction box, the kitchen was previously on the downstairs ring circuit but there was a new kitchen ring ran for the big fancy kitchen with full splash back, the cupboard that was blanked off was in the kitchen so i fear the problem may be in there.
 
Thanks for the quick reply. Yes i checked for trapped insulation. My thinking is junction box, the kitchen was previously on the downstairs ring circuit but there was a new kitchen ring ran for the big fancy kitchen with full splash back, the cupboard that was blanked off was in the kitchen so i fear the problem may be in there.

Is the customer willing to pay for you to spend the time fault finding?
 
Yeah thats what i think.
i have a feeling the customer wants me to tell him it will be ok to leave as it is. There wont be much load on it the circuit. A couple of tvs, table lamps and a phone. But a bad connection is still a bad connection. I dont know what else to tell the guy. I dont want to leave it
 
Yeah thats what i think.
i have a feeling the customer wants me to tell him it will be ok to leave as it is. There wont be much load on it the circuit. A couple of tvs, table lamps and a phone. But a bad connection is still a bad connection. I dont know what else to tell the guy. I dont want to leave it

The customer can want as much as he desires...tell him your findings,offer the option of curing it,and do as instructed...these issues occur everyday and all that is required of your good self,is to be honest,polite,and move on...:28:
 

Reply to High resistance on ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock