Discuss High Voltage at Breaker Box in the USA area at ElectriciansForums.net

vhfuguet

DIY
Reaction score
0
my tester reads 146v both hot wires with the neutral measured at the breaker box, but oustside in the meter is 118v, why?
 
TL;DR
My voltage is 148V at breaker box, but power company says it's ok at the meter
What is the voltage reading between the two hots?

Is there any load drawing current from the panel or just your tester?
 
298V is not far from twice 148V so the readings are consistent and not suggestive of faulty wiring. Did you measure the 118V with the same meter? I suspect it may be giving misleading readings. What led you to check the voltage?
 
Strong suspicion that your multimeter is malfunctioning. Suggest testing with something else. Do you have symptoms of incorrect voltage: equipment failing, overheating, lights flickering or blowing, thermal cutouts tripping?
 
Check the voltage rating on its power brick or wall wart. Most are designed for worldwide use and will operate correctly anywhere between 90 and 254 volts. Even if it only carries UL listing for operation at 120V. My hunch is this is not the problem, unless the voltage is fluctuating wildly.

At 150V anything with a wirewound transformer or induction motor would be humming more loudly and running very hot. Heating elements will be giving nearly 40% more heat as it is the square of the voltage that matters. It's not impossible but with the PoCo guys saying it's 118V I am not convinced by your multimeter reading.
 
Suggestion #1 try you meter at someone else's home

Suggestion #2 get another meter of known provenance and compare them to see if they agree to around 1% or your one is simply giving crazy results.
 

Reply to High Voltage at Breaker Box in the USA area at ElectriciansForums.net

Similar Threads

Hi ive recently got myself a mig welder for my garage but each time i try to use it it trips out. Ive spoken to an electrician and he said its...
Replies
25
Views
699
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
862
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
678

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock