tomspark93

-
Esteemed
Reaction score
339
So I have a job to quote for installing an outdoor sub main. It's in quite a rural location and the supply seems to be TNCS. However, there is another conductor that leaves the MET and looks like it could possibly go to to a rod (the cable that leaves through a hole just to the left under the meter tails) This might be part of the DNO's earthing if its end of line I guess.

I've measured Ze at 2.72 ohms. Where do you stand in regards to cable calcs? Obviously first port of call is to ring the DNO and see what their stance is on it.
However, if they are disinterested whats the best port of call? It doesn't seem right designing a circuit that cant meet disconnection times. I know TT installs we'd use RCD's to meet the requirements for fault protection. Would it be the same in this instance?

The covers are only off them henley blocks for testing purposes:p

tigers.jpg
 
I couldn’t see where the pole was unfortunately. There was heavy greenery behind the existing meter cabinet which is externally located at the end of a track. I’ll nip up tomorrow and have another look as it’s not far from where I am working.

The sub main is potentially going to a steel frame around 160m away which will feed the rugby clubs new electric score board and from there it will potentially branch off to feed a couple of heaters in the dugouts and also a socket in a camera stand.

Overview.png
 
Last edited:

Reply to High Ze Cable Calcs 20 characters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
Replies
2
Views
1K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock