Discuss Cable calcs zs and ze values in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
22
Cable calcs using cable calc app
Working out cable size for a workshop.
100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own, tt earth on 300ma rcd.- 20 ohms

App says 50mm swa which I expect.

But if I alter earthing to tncs 0.35 ohms it says max ze exceeded zs of device.

Am I missing something here / Friday afternoon brain.

Thanks
 
For TT, the app is using the RCD for protection against earth faults, as you would - the OCPD almost certainly would not operate for fault currents on a TT system.

When changed to TN-C-S, it appears the app has decided to use the OCPD for protection against earth faults. However you can use an RCD for this protection on TN systems, it's perfectly acceptable (all other things being correct)
 
For TT, the app is using the RCD for protection against earth faults, as you would - the OCPD almost certainly would not operate for fault currents on a TT system.

When changed to TN-C-S, it appears the app has decided to use the OCPD for protection against earth faults. However you can use an RCD for this protection on TN systems, it's perfectly acceptable (all other things being correct)
Thanks
Always wondered what people do when device operating zs is lower than ze. Never practically come across it till now.
 

Reply to Cable calcs zs and ze values in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
896
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock