Discuss High ZE on a tns system in the Industrial Electricians' Talk area at ElectriciansForums.net

D

davedwr1978

Hiya guys, looking for a bit of advice, I went to carry out an eicr Friday and it's a tns system but I'm getting 87 ohms I took the clamp off and cleaned it up gave it a good tightening but still no difference, any idea what I can do now??
 
The first thing to do is thank your lucky stars you didn't damage the PILC cable by giving the clamp a good tightening!
Inform the DNO and get them out to fix the situation, I wouldn't mention that you've been interfering with it though, they might take exception!
I assume it is a proper lead clamp and not a pipe clamp?
 
Ring dno i had same situation on my assesment the dno charged 60 quid for a new isolator and make into a pme system. in the meantime i made temp tt system got it down to 42 ohms good for one rod.
 
Right guys my mistake, I MEANT. That I tightened the bolt that connected the 10mm Earth to the clamp as it was a bit loose, but I cleaned up the surface of the bolt, no need to be a bunch of arse holes, it was a bit of advice I needed, it must be amazing to know everything and never have to ask for advice, that's what I thought this site was about, and mate don't call me stupid you muppet, as for the guys who answered without cocky attitudes THANKYOU FOR YOUR ADVICE
 
Right guys my mistake, I MEANT. That I tightened the bolt that connected the 10mm Earth to the clamp as it was a bit loose, but I cleaned up the surface of the bolt, no need to be a bunch of arse holes, it was a bit of advice I needed, it must be amazing to know everything and never have to ask for advice, that's what I thought this site was about, and mate don't call me stupid you muppet, as for the guys who answered without cocky attitudes THANKYOU FOR YOUR ADVICE


You will not get far with an attitude like that to be honest.
 
You will not get far with an attitude like that to be honest.
ATTITUDE!!! I think I have the right to stick up for myself, it was an honest enough question, I don't appreciate the mocking mate, everybody needs a bit of help sometimes, I hope one day you will be subject to this see what your reply would be, there's no need of it
 
Right guys my mistake, I MEANT. That I tightened the bolt that connected the 10mm Earth to the clamp as it was a bit loose, but I cleaned up the surface of the bolt, no need to be a bunch of arse holes, it was a bit of advice I needed, it must be amazing to know everything and never have to ask for advice, that's what I thought this site was about, and mate don't call me stupid you muppet, as for the guys who answered without cocky attitudes THANKYOU FOR YOUR ADVICE


You need thicker skin matey
 
Right guys my mistake, I MEANT. That I tightened the bolt that connected the 10mm Earth to the clamp as it was a bit loose, but I cleaned up the surface of the bolt, no need to be a bunch of arse holes, it was a bit of advice I needed, it must be amazing to know everything and never have to ask for advice, that's what I thought this site was about, and mate don't call me stupid you muppet, as for the guys who answered without cocky attitudes THANKYOU FOR YOUR ADVICE

How are we to know what you meant? We only have what you have written to base our answers on.

If you think a post is out of order then there is a report button which will get the moderators to have a look at the post.
 
Last edited:
Thread closed due to Op being banned.
 

Reply to High ZE on a tns system in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
High Ze on a tns supply. It’s 1.48 ohms. Weird as I did a Ze here 4 weeks ago and it was 0.50. Do DNO come out for a Ze that high what is likely...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock