- Reaction score
- 4,243
Ouch! Hope you didn't get hurt too badly.So did I until I stepped onto ice completely covered in snow!
Discuss High Zs reading in the UK Electrical Forum area at ElectriciansForums.net
Ouch! Hope you didn't get hurt too badly.So did I until I stepped onto ice completely covered in snow!
Hi - the max loop impedance for BS1362 fuses can be found in BBB Table 41.2 (d) . This gives 2.3 Ohms for 13A, so 80% is 1.84 Ohms. So looks ok .the second question is regarding the same circuit, they have a fuse spur fed from one of the sockets and then have 6 x double sockets after the fuse spur. The last 3 are out door and the last socket on the ‘radial’ gives a Zs reading of 1.64.
Pride onlyOuch! Hope you didn't get hurt too badly.
It says on the inside of my EICR certificate book that 1.08 is the max Zs value allowed on a type B 32 amp MCB. Is that correct?The generic values for the cpc compared to the live conductors is 'live value' x ( live x-section/cpc x-section)
So
2.5/1.5 = 1.667 as above
2.5/1.0 = 2.5 ( with 0.41 gives 1.025)
How are you calculating the Zs as 1.08?
In the ring r1 + r2 should be (R1+R2)/4
This should be added to the Ze value to give the r1 + r2 for all sockets on the ring, but the radial off the ring would not be this value.
It would be this value plus the measured r1 + r2 of the radial portion.
Whatever value you get for the zs on the radial may be above the allowed value for the OCPD feeding the ring, but below the allowed value for the 13A fuse
I’m not there now but I think it was 2.5/1.5 cable but you have got me thinking now.Is this an old install with 1.0mm cpc?
Roughly for the figures given for the L&N, cable length would calculate to approx 62 metres
the cpc should calculate to approx 0.72 for a 1.5mm and 1.08 for a 1.0mm
you may even get a lower reading on the cpc if there are any parallel earth paths.
Yes, that would be the correct limit for the ring and the spur up to the fuse.It says on the inside of my EICR certificate book that 1.08 is the max Zs value allowed on a type B 32 amp MCB. Is that correct?
if the radial off the ring via the spur is higher than 1.08 but less than the allowed value after a 13amp fuse, which value would you write on the test form?
Thanks
Excellent. Would you write that result on the test form and mention the fuse spur somewhere? Thank youHi - the max loop impedance for BS1362 fuses can be found in BBB Table 41.2 (d) . This gives 2.3 Ohms for 13A, so 80% is 1.84 Ohms. So looks ok .
Thank you for your help.Yes, that would be the correct limit for the ring and the spur up to the fuse.
From the fuse onwards, it isn't protected by the mcb, but by the fuse, so you need to use the appropriate value for that, think it's about 80% of 2.3 ohm, I haven't got my book around.
As for the eic/eicr depends on your software, but I would add an additional line below the rfc entry (no circuit in the cu) detailing the radial off the rfc as a seperate entity but not from the cu mcb
The use of 2.5/1.0 was around the 14th I think, way more than 15 years ago unless there was another phase of use
Reply to High Zs reading in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.