Discuss Honeywell Accenta zone problem!! in the UK Electrical Forum area at ElectriciansForums.net

TheCodboy

-
Arms
Reaction score
109
Just installed a Honeywell Accenta alarm and having some trouble with a zone. Basically, when the alarm is set and the front door contact is broke, the alarm gives me time to put the code in to deactivate. Unfortunately the PIR in the hallway is activated and triggers the alarm to go off fully. Ive set the hallway zone to be timed,just like the door contact but it still causes the alarm to sound. First time doing an alarm...... probably my last!!!
 
onlyproblem with programming the hall PIR as entry inhibited is if it's the first detector to be triggered on coming downstairs. it needs to be progged E/E when system is part set.
 
you can either prog it as E/E all settings, or, for greater security. prog. inibited on full set, and e/e on part set (if the control panel will allow that. some of the cheaper panels won't).
 
Yep, on the Accents Gen4 you can programme area 2 so that on part set, intermediate/inhibit zones become entry/exit ( in addition to the normal entry exit. Make Z1 entry/exit and Z2 the inhibited zone.
 
Just fitted an accenta G4 but having problems setting it up, I got it all up and running but I can enter my garage without disarming the alarm and it takes around 3 minutes to activate the siren, also my pir flashes red when I move but the alarm does not sound.
Any help would be appreciated as it's driving me mad.
 
Just fitted an accenta G4 but having problems setting it up, I got it all up and running but I can enter my garage without disarming the alarm and it takes around 3 minutes to activate the siren, also my pir flashes red when I move but the alarm does not sound.
Any help would be appreciated as it's driving me mad.

Welcome to the forum mate.
Sounds like you have the garage PIR wired into an 'entry zone'
Try wiring it into one of the last zones and see if that fixes it.
 

Reply to Honeywell Accenta zone problem!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All Qualified electrician, usually stay away from alarms but my friends parents have issues. Texacom Vertas panel, not worked for over 3...
Replies
2
Views
1K
I know this is a forum for electrical problems but I can't find a forum for burglar alams (is there one?) Bye the by one of you may have an...
Replies
0
Views
1K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
I have just installed a Honeywell Accenta G4 system. All ok apart from 2 queries: The entry/exit zone 1 is a PIR (there are no door contacts on my...
Replies
4
Views
3K
My burglar alarm went off last night when it wasn't even set. When I went to Keypad it was showing TAMPER with a Red light. I could not silence it...
Replies
16
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock