Discuss Honeywell st699 to st9400c wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello I have a question switching the above central programmers. I seem have a few more wires than other examples I’ve seen online.

For instance I have 3 wires in terminal 1 (brown and 2 red: one is a bridge to terminal 5 which I believe would be discarded); also have 3 wires into terminal 2 ( 2 blue and 1 black). This setup seems to have more wires than other examples. Can anybody guide me on how to switch over to the st9400c?

Thanks in advance.
 
Photo of current wiring attached.
 

Attachments

  • C18DA4DE-F62D-4F66-8BA4-7BB1FC392AE9.jpeg
    1.2 MB · Views: 12
The st9400c installation manual has a terminal by terminal replacement guide chart for swapping a 699 to a 9400c
It's available here if you don't have it in the box for some reason.

If an existing terminal has more than 1 wire all those wires must go in the new terminal (except the links in terminals 5 and 8 as they are internal in the 9400c)
 
The original wiring is all 'old' colours, including one of the blues, which is part of a red/blue/yellow cable.
There appears to have been a 'new' colour wire added at some time - a blue/brown flex, which may or may not be a bodge, so proceed with caution.
There's also no sign of any earth wires in your pic. Unless the wiring is really old, each of the cables should have one, and they must all be connected together..
 
The old unit appears to be fitted to a flushed in back box so hopefully the earths are connected to the earth terminal there.
 
The st9400c installation manual has a terminal by terminal replacement guide chart for swapping a 699 to a 9400c
It's available here if you don't have it in the box for some reason.

If an existing terminal has more than 1 wire all those wires must go in the new terminal (except the links in terminals 5 and 8 as they are internal in the 9400c)

Thanks, any terminal with more than 1 wire went into new terminals. Fitted and working. Thanks.
 

Reply to Honeywell st699 to st9400c wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, We have recently replaced our central heating programmer with a Honeywell ST9400C. We now want to replace our old wireless room...
Replies
0
Views
696
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
667
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
I would like to replace my ancient Honeywell mechanical thermostat with a Honeywell T3R PROGRAMMABLE THERMOSTAT I have three wires in the old...
Replies
1
Views
3K
Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
518

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock