Hi all im looking for some advice on installing a hot tub, the supplier specifies a 16 amp type c mcb, a 20 amp rotary switch and an ip rated 13 amp socket with rcd protection, the run of swa cable from the consumer unit to the rotary switch is 30m, I will then run an swa from the rotary switch to the ip rated 13amp socket for the hot tub to be plugged in direct, what im needing advice on is the voltage drop, the cable will be clipped direct to a wall, 30m run, ive worked it out that there will be a voltage drop of 10.5v which works out at a vd of 4.6%, do yiu agree that a 2.5mm swa cable will be more tham man enough to run the hot tub, cheers.
 
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
 
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi the hot tub only draws 13amps as its a plug and play,
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi the hot tub only draws 13amps its a plug and play cheers
[automerge]1593455281[/automerge]
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi Ive worked out the voltage drop to be 7.41 volts, mV/a/m x Amp x Metre /1000 = 19 x 13a x 30meters /1000 = 7.41 vd
 
Last edited:

Reply to hot tub installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
417
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Hi, looking for some advice, 6mm swa allready installed to a hot tub Client now wants additions and my calcs say the original swa is allready too...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock