Discuss How not to standard is this rewire? in the UK Electrical Forum area at ElectriciansForums.net

I think there is a bit of crossfire here where @davesparks is using 'testing' to mean taking measurements (distinct from inspection) while others are using it as shorthand for 'carrying out an EICR.' I agree with him that evidence to support an argument in favour of rewiring usually comes from the inspection. An exception from my experience was a church wired in imperial MI, which looked in good condition at its first ever EICR. However IR tests revealed that almost every cable run was catastrophically low in insulation and that there were hardly any intact seals in the whole building.

I also agree that there are situations where a rewire is requested or justified on strategic grounds that are independent of the condition of the existing wiring. I.e. that rewiring is clearly a valid approach even if the existing would give a satisfactory EICR.

Hopefully @JimCee will be back soon with the EIC
I see both sides, i just wonder why, if wiring is perfectly fine, would we need to run in more wire? Seems wasteful in this day and age. If stuff's outdated and the wiring is testing fine, why can't we just update peripherals and other stuff, what advantage does running in completely new wire give?
 
I can't agree with this, you don't need an EICR to know whether an installation needs to be rewired.

A good point; I didn't phrase that well, and partially contradicted it in post 58. What I meant was there is no simple rule of thumb along the lines of 'Wylex fuse box -> rewire is mandatory.' The installation must be viewed as a whole by someone competent to carry out an EICR, and in some cases the economics might indeed justify a full EICR, to decide the best course of action.
 
I see both sides, i just wonder why, if wiring is perfectly fine, would we need to run in more wire? Seems wasteful in this day and age. If stuff's outdated and the wiring is testing fine, why can't we just update peripherals and other stuff, what advantage does running in completely new wire give?

If it is indeed perfectly fine then there is likely no need to replace it.

But if it is perfectly fine then the chances are that an electrician hasn't been employed in the first place.
 
I don't see how it can be obvious that potentially perfectly good copper cabling needs to be replaced with new copper cabling without any detailed testing of the wiring.

How can you possibly tell if copper wiring needs to be replaced without being able to see it and not performing testing on it? Makes no sense.
 
I don't see how it can be obvious that potentially perfectly good copper cabling needs to be replaced with new copper cabling without any detailed testing of the wiring.

How can you possibly tell if copper wiring needs to be replaced without being able to see it and not performing testing on it? Makes no sense.
It is very easy to sum it up in one word EXPERIENCE!!!!
 
How can you possibly tell if copper wiring needs to be replaced without being able to see it and not performing testing on it? Makes no sense.

Why limit this to copper?

No you can't tell without seeing it, that should be obvious and I don't think anyone has suggested that you can make any assessment without seeing the installation.

My point is that you can often tell if a full rewire is required based on an inspection alone.

I'll take a domestic installation as an example.
The customer wants your opinion on the installation and a quote to change a couple of rooms to downlights, add extra sockets in every room because there's only 1 in each room, replace all switches/sockets with some trendy shiny metal.

You unscrew a few pendant caps and find imperial twin with no CPC.
The CU is a wooden backed wylex, a little bit loose on the wall as the wooden wall plugs have shrunk over the years. 5 circuits, cooker, ring, immersion heater, lights up, lights down.
There's 1 ivory single socket in every room with plate screws top and bottom.
Bonding is a rather skinny bare tinned conductor half-arse wrapped around a water pipe.
The immersion heater circuit has been attacked by a plumber to feed a shower pump and a replacement boiler.
The attached garage has all the typical DIY additions with round joint boxes and dangly cables.
There's probably even a greenhouse somewhere with a plastic twin socket on the wrong pattress and a rusty old tubular heater.


I'd go out on a limb and say that it's probably going to be better to rewire it than try to bring it up to current standards.

The lighting needs a cpc added to all points so you may as well rewire it as mess around trying to add a CPC.
The ring really needs splitting in to two circuits and by the time you've done that and extended to to all the new points there'll be so little of the original installation left that you might as well have rewired (plus it would be cheaper and quicker)
 
@davesparks example was better than the one I was creating!

I never enjoy the question "do you agree that this house needs a rewire?".
For what it's worth, in my opinion the need for a rewire seems to more often come down to the degree it's been monkeyed around with and whether the intended outcomes would be more easily done if starting again rather than the age of the wiring or condition of the wiring.

Even poor IR results don't instantly mean a rewire as they could be low for other reasons. Faulty appliances, outside lights, and borrowed neutrals can very quickly make an installation look dire when testing it!
 
The work in the pictures is shocking (pun intended)

if your son doesn’t want to share the contractors details with you, perhaps he could join the forum and post a copy of the certificate here with the details removed?

also, some advice is better taken from an independent professional than a family member.
This is the main bits of the certificate I got from him 👍🏽
 

Attachments

  • AE0BD876-FBEF-420F-B684-05679D77F143.jpeg
    204 KB · Views: 66
  • FFBDB2D6-0161-47DE-A1B8-D7523A4DAF79.jpeg
    224.1 KB · Views: 63
If you want a big job like a rewire done next week then you have to accept you are not going to get the best job because the guy's doing a good job are generally booked up for weeks or months in advance also the £3K price should set the alarm bells going
Tbf I would’ve paid more…but I got 3 quotes, 2 being £3500 & the third was this fella who said he could get it done in a day for £3150 - said he puts all his lads on it which is why he can get it done so quickly - but thought this was around the right price with 3 people quoting it.
 
Tbf I would’ve paid more…but I got 3 quotes, 2 being £3500 & the third was this fella who said he could get it done in a day for £3150 - said he puts all his lads on it which is why he can get it done so quickly - but thought this was around the right price with 3 people quoting it.
No RCD trip times but all the test buttons operate???
No IR results.
Arc fault protection on EVERY circuit.
That certificate is as dodgy as the wiring.
 
Short circuit capacity of supply fuse 100KA.
seems like a made up number to me!
I am suspicious about some of the other test results, they seem to good to be true.
 
No RCD trip times but all the test buttons operate???
No IR results.
Arc fault protection on EVERY circuit.
That certificate is as dodgy as the wiring.
Obviously my electrical knowledge is minimal so I just assumed everything was right - I’ve had a plasterer in already 🤦🏽‍♂️ Is there a way to test everything rather than having to rip everything out again?
 
Exactly what I thought when reading the OP and wondered if they work in the north of England?
The 1 day Re-wire guy from Scotland him and his team appeared to do work to a reasonable standard , a bit rough when it came to chasing out walls but I don;t remember seeing him bury connector strip in the walls and under the skirting boards

The 1 day re-wire in this thread looks like it was done by people who just didn;t give damn
 

Reply to How not to standard is this rewire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
809
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
812
Hi, Hopefully I haven't made an error but I was speaking with another electrician and he said standard junction boxes with screw terminals can no...
Replies
3
Views
851
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
403

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock