Discuss How tight is tight. in the Industrial Electricians' Talk area at ElectriciansForums.net

Kyran

-
Reaction score
11
Ok so we all know we should do good connections, tight so they don’t creep out of create loss connections.


I know that there is a specified newton tightness but looking in the BGB I can’t see the value and i looking in the wrong place.


reg 526.1 “every connection between conductor or between a conductor and other equipment shall provide durable electrical continuity and adequate mechanical strength and protection.”


Thats all great but how tight should it be?


Can anyone point me at the right reg/value.


Thanks
 
All connections should be tightened to the torque stated in the manufactures instructions, there isn't a one value suits all for what a connection should be tightened to.


So it is, just looked in the the box of a waterproof CU i have in the cupboard and sure enough in the first flap "installation" its as terminal bar 1-1.5 Nm and RCD/MCB 2-2.5Nm

Should have look there first

Thanks. Its just one of those regs that just refers to to the manufactures. Ops thanks peps.
 
So it is, just looked in the the box of a waterproof CU i have in the cupboard and sure enough in the first flap "installation" its as terminal bar 1-1.5 Nm and RCD/MCB 2-2.5Nm

Should have look there first

Thanks. Its just one of those regs that just refers to to the manufactures. Ops thanks peps.


well they weren't going to exactly list every make and model of consumer unit along with the required torque setting in the BGB/BYB were they lol
 
I've never used a torque screwdriver, and I've never envisaged having to use one in a domestic situation.
I always thought it was something you just get a feel for, like knowing how much pressure to apply on a cable to strip the insulation off but not cut right through it.
 

Reply to How tight is tight. in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
842
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
How does a terminal become completely loose? My uncle had an old school outside socket installed ~40years ago he asked me to have a look as it...
Replies
10
Views
4K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock