DMRW

Domestic work not my usual field however a "friend" is having their extension done and asked me to help with wiring etc.
I was double checking what size cable for the cooker point and he said that above the ceiling he has 6" joists and will be having 6" of insulation squeezed in. How do I get around the severe de-rating factor that brings? Don't fancy making 16mm of into a cooker point! It appears to me part P and the new part L regs don't agree.
HELP
 
If you cant avoid the insulation then im afraid you have 3 options ...

-MICC .... a dying skill but would see vast reduction in size
-Do the run in 16mm then derate from cooker switch to outlet Your front end device will still be protecting the smaller size cable but i would note it on the cert'.
-Tell your friend your busy and unfriend . him on FB ;)
 
Thankyou for your answers.
Mi would be perhaps a little unorthodox for a domestic extension although a little tempting. And with regards to unfriending him. I'm on loan to an estates department and am sort of paired up with him as he was historically the lamp changer. Might make work a little awkward. Running in 16mm and derating not a huge fan of that but could be the solution.
Murdoch - I know part p is mostly about registration and competency but I assume please correct me if I'm wrong that it states work should be carried out in line with bs7671? Which gives the derating factors etc. And is part L not all to do with energy efficiency and insulation values?
Ample current - running the cables under the insulation gives me two concerns
1st wouldn't that be very similar to running in insulation anyway. Its going to be squeezed in as the joists are a few mm smaller than chosen insulation.
2nd getting through the joists has to be done 50mm from top or bottom bringing my cables out the joist into the centre of the insulation.
Opinions?
 
if you haven't done cable calcs yet, what length of run, rating of appliance, grouping etc.? is it flat roof extension, any other poss routes?
 
It is a dorma bungalow being extended on the side with garage utility etc downstairs master bedroom upstairs in the roof. Haven't been to job yet but have plans. From plans and discussions with client it seems every suggestion I put to him has insulation added on top. Oh I plan to make that a room at the end. Or its involved in the extension I'll have to insulate under the floor there too.
Length of run obviously depends on final route but the best route discounting insulation is 15m. Its for a general cooker point. Which means I want it as high a rating as possible. The board I'm coming off can have either a 40a or 50a breaker fitted. 50a supply to cooker will be unachievable so was hoping to be able to use the 40a breaker.
 
i think 16mm is good for around 20kw using info supplied (won't take long for someone to correct me if wrong!) which seems rather alot. did you apply diversity? hope u get it sorted.
 
Go and LOOK at the place yourself first, before you start making assumptions of what can and can't be done. I'd be surprised if the vast majority of this cable run, can't be run outside of any insulation in a bungalow type installation. Maybe even take a few photo's that you can post up here...
 

Reply to How to avoid insulation under the floor? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock