hi all,
looking for some advice please on how to carry out an r1+r2 reading on a 35.mm,(3p+n)4 core,swa cable. it is a sub main cable with a parallel 35.mm cpc. however both ends are terminated into a steel main panel,and a steel distribution board respectively, with a number of other parallel earth paths. the installation is also galv conduit and steel trunking continuous and all linked back to main panel/distribution boards.
i believe that i would have to disconnect both glands of the 35.mm swa and parallel 35.mm cpc from both ends,and link across each phase (individually) to parallel 35.mm cpc to get my true r1+r2 reading.
(not practicable i know) but was just double checking .

hope you can help
many thanks
deano
 
Easiest thing to do is forget about R1+R2 and just do an R2 with a wander lead.
 
just link the seperate 35mm cpc to any of the 3 lives at the DB and measure the reading at the panel board.
its not practical to physically disconnect the cable at both ends , for a periodic anyway.
 
thanks biff 55.
if the parallel cpc was only 10.mm could i still carry out the test in the same way you advised or would i need to take into account the steel wire armour. again i do appreciate in an ideal world.
cheers
deano
 
the seperate earth is performing the task of cpc not the swa , otherwise theres no point it being there.
although the glands and steel enclosures will help bring down the Zs by providing additional earth paths , the pvc 35mm is still the R2.
 
thanks biff 55
i thought maybe the 10mm parallel cpc was too small, and i would have to take into account the swa as part of a true r1+r2 reading, or is it fair to say that this would be ok for reading/cert as we obviously have additional cpc csa with regard to swa also being used.
thanks again
cheers
deano
 
If its a particularly long run then I might make the connections in the DB. Since the armour is bonded with a fly lead with the cpc conductor to the earthing bar, then I would have thought that a jump lead across from L1/L2/L3 of the mcb to the earthing bar and just measure at the load end .

However, an interpretation of a 'true' R1+R2 is more likely to be the reading with everything connected up as this under fault conditions will be the true fault path.
 

Reply to how to carry out r1+r2 reading on swa in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, Hoping to get some advice on R1 + R2 radial testing and best practise. When doing R1 R2 instead of taking cables from mcbs/rcbos and the...
Replies
1
Views
2K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock