Screenshot_20231129_183630_Samsung Notes.jpghi all just got a Q regarding how to find R1 then second Q how to find R2 what i did so far was mutiplying each answer for1.67 so I could get the answer for R2 is there a easy way to find R1 without kinda guessing TIA .
 
The 1.67 multiplier only works for 2.5 line conductor with 1.5 protective conductor. The cable specified is 4mm line conductor with a 1.5 protective conductor. You should be able to work out what multiplier to use in this case.

How to find the r1 value? By using the on-site guide tables.
 
The 1.67 multiplier only works for 2.5 line conductor with 1.5 protective conductor. The cable specified is 4mm line conductor with a 1.5 protective conductor. You should be able to work out what multiplier to use in this case.

How to find the r1 value? By using the on-site guide tables.
4mm L 1.5cpc 16.71
 
Okay so you have the Table. From this you can calculate r1 and r2 separately. What you have done from your figure and looking at the Table is put r1 and r2 in parallel.
Just to add continuity for a ring final is lower case so r1 not R2.
 
The Table is a bit misleading. A 1.5 conductor will have the same resistance whether it is r1 or r2. Use the line column for the 1.5 cpc.
 
Alternatively take the 16.71 for 4.0/1.5 and deduct 4.61 for the 4.0 and this will give you 1.5. Same result either way.
 

Reply to How to find R1 and R2 separately in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...
Replies
7
Views
487
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock