I am looking to join 2 cables for an outside security light. The mains cable on the existing light is 8mm flat twin. But the new light is a 6mm round twin.

I can't rewire as it goes into the wall to the socket. So was looking at an ip66 connection. But can't find one that does both sizes.

Any advice appreciated.
 
From your description I believe the flat twin and earth is 1.5mm2 (make sure there is an earth... a bare copper conductor between the other two)
The round flex will be 1.0mm2

There should be ip rated joint boxes that cope with both. Any local wholesaler should be able to help.
 
You could perhaps use a Wiska box, e.g. size 308, they come in a few colours, I typically use black outside but sometimes white or cream.

These boxes take screw-in glands, 20mm dia., and you can get glands for various diameters of round cables, also glands for flat twin & earth (1mm2, 1.5mm2, etc).
 

Reply to I want to join an 8mm flat twin cable to a 6mm round twin. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K
Hi, I purchased a Time twin strand bell cable with a rating of 12-30V, 2A, low voltage, not for mains use. I wish to use this for installing our...
Replies
4
Views
792
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hi.... First time I've posted here. I own a property which is rented out. Recently the Gas Oven failed a gas safety test and the Gas Engineers...
Replies
4
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock