IMIT TWIN THERMOSTAT (LONG PROBE) hi just wondering if anyone can explain the wiring diagram for this thermostat. The question has been asked before but I can get the information I need. I have asked an electrician but he’s unsure.​

 
It's 2 thermostats in series.
1 Stat is manual reset (for overtemp)
The other is the control stat for adjusting the operating temperature.

What's the problem, has a new one been fitted incorrectly?

Dual stat.PNG

Dual stat wiring.PNG
 
It's 2 thermostats in series.
1 Stat is manual reset (for overtemp)
The other is the control stat for adjusting the operating temperature.

What's the problem, has a new one been fitted incorrectly?

View attachment 94194

View attachment 94195
Thank you snowhead for the help. I feel I have info I need to do the job. I’m getting too old and the brain ain’t what it used to be. The old one packed in and I’m waiting too long for an electrician. It wouldn’t be a problem but for the weather.
 
Hi guys, would really appreciate your help here. I'm a plumber and have to change one of these thermostats soon. Could someone please tell me which terminal I connect the live and neutral wires to? I'm sure live is connected to C on the left of the diagram but unsure with the negative. Thanks Tom
 
Hi guys, would really appreciate your help here. I'm a plumber and have to change one of these thermostats soon. Could someone please tell me which terminal I connect the live and neutral wires to? I'm sure live is connected to C on the left of the diagram but unsure with the negative. Thanks Tom
The 'negative', or rather neutral, doesn't go to the thermostat at all, it goes to the load.
Live is connected to C as you say, and then the switched live from terminal 1 of the adjuster goes to the load you want to switch off when temp is reached (assuming that's what you want to do!)
 
Last edited:
The 'negative', or rather neutral, doesn't go to the thermostat at all, it goes to the load.
Live is connected to C as you say, and then the switched live from terminal 1 of the adjuster goes to the load you want to switch off when temp is reached (assuming that's what you want to do!)

The 'negative', or rather neutral, doesn't go to the thermostat at all, it goes to the load.
Live is connected to C as you say, and then the switched live from terminal 1 of the adjuster goes to the load you want to switch off when temp is reached (assuming that's what you want to do!)
I'm still a little confused, so where would I connect the blue (neutral wire) please. Obviously the live, neutral and earth wires are all in one cable. Would I connect the neutral wire to 1 U on the far right off the diagram? Yes I want the load to switch off when temperature is reached
 
I'm still a little confused, so where would I connect the blue (neutral wire) please. Obviously the live, neutral and earth wires are all in one cable. Would I connect the neutral wire to 1 U on the far right off the diagram? Yes I want the load to switch off when temperature is reached
Sorry I didn't get where you were coming from with the reference to 'neutral'.

Normally the three core cable is carrying live to the thermostat, and the neutral/ blue wire, as you suggest, is used to carry the switched live back to the wiring centre, or whatever it is connected to.
If done properly the blue wire should have a brown sleeve or brown tape over the exposed blue insulation, to indicate this Is carrying live when the switch is closed, but it sounds like yours doesn't have that! Good idea to add it!

If you are doing a like-for-like replacement, then what you suggest - blue wire to 1U - is correct.
On the other hand if your cable is actually connected to live and neutral at the other end, eg a 13A plug, then BANG!
 
Sorry I didn't get where you were coming from with the reference to 'neutral'.

Normally the three core cable is carrying live to the thermostat, and the neutral/ blue wire, as you suggest, is used to carry the switched live back to the wiring centre, or whatever it is connected to.
If done properly the blue wire should have a brown sleeve or brown tape over the exposed blue insulation, to indicate this Is carrying live when the switch is closed, but it sounds like yours doesn't have that! Good idea to add it!

If you are doing a like-for-like replacement, then what you suggest - blue wire to 1U - is correct.
On the other hand if your cable is actually connected to live and neutral at the other end, eg a 13A plug, then BANG!
what if the blue were connected to the common and then brown to 1.....what would happen?
 
what if the blue were connected to the common and then brown to 1.....what would happen?
It all depends on what the blue wire is connected to at the other end of the cable.
People have been referring to it as 'neutral'. If that is what it is, the answer to the question is "BANG'
If it is actually the switched live going to the load (U in the diagram) - in which case it should have a brown tape or sleeve on the wire - it should work!

Just to recap on the diagram:
It shows two things - there is a very faint grey line showing a box around the thermostat bit. That is the extent of what you have in the thermostat. Terminals labelled '1', '2' and 'C'.

The two 'U' boxes are not in the thermostat, each 'U' is a representation of a possible load (eg immersion or valve) to be controlled
So if you want to switch something off when the thermostat is hot enough, you take a wire from right hand terminal 1 (in the diagram, which is a switched live) to the thing you want to switch. It will be a live wire to feed the load, and the other side of that load needs to be connected to 'neutral'.
You need to find out if your blue wire goes to the live side of the thing you want to switch on/off, in which case it's not a neutral wire, it's a switched live, and the blueness is misleading.
Or is it actually a neutral? I suspect not, but I would test it with a meter first,
 
It all depends on what the blue wire is connected to at the other end of the cable.
People have been referring to it as 'neutral'. If that is what it is, the answer to the question is "BANG'
If it is actually the switched live going to the load (U in the diagram) - in which case it should have a brown tape or sleeve on the wire - it should work!

Just to recap on the diagram:
It shows two things - there is a very faint grey line showing a box around the thermostat bit. That is the extent of what you have in the thermostat. Terminals labelled '1', '2' and 'C'.

The two 'U' boxes are not in the thermostat, each 'U' is a representation of a possible load (eg immersion or valve) to be controlled
So if you want to switch something off when the thermostat is hot enough, you take a wire from right hand terminal 1 (in the diagram, which is a switched live) to the thing you want to switch. It will be a live wire to feed the load, and the other side of that load needs to be connected to 'neutral'.
You need to find out if your blue wire goes to the live side of the thing you want to switch on/off, in which case it's not a neutral wire, it's a switched live, and the blueness is misleading.
Or is it actually a neutral? I suspect not, but I would test it with a meter first,
I meant with the blue wire as a switched live going to the load. infact what I was asking what would happen if I vice versa the connection and put brown (incoming live) to 1 and my blue (switched live) to C. How would the thermostat behave?
 
I meant with the blue wire as a switched live going to the load. infact what I was asking what would happen if I vice versa the connection and put brown (incoming live) to 1 and my blue (switched live) to C. How would the thermostat behave?
If you mean the No1 contact on the right of the diagram in post #3, then it should work fine as a thermostat that switches off when it gets hot.
You are presumably not talking about the limiter No 1 contact on the left, which turns on when the limit stat reaches temperature.
 
If you mean the No1 contact on the right of the diagram in post #3, then it should work fine as a thermostat that switches off when it gets hot.
You are presumably not talking about the limiter No 1 contact on the left, which turns on when the limit stat reaches temperature.

If you mean the No1 contact on the right of the diagram in post #3, then it should work fine as a thermostat that switches off when it gets hot.
You are presumably not talking about the limiter No 1 contact on the left, which turns on when the limit stat reaches temperature.
I have a thermostat that doesn't cut power at set temperature. What could be the problem?? I was suspecting the connection but as you say it may not be the issue
 
I have a thermostat that doesn't cut power at set temperature. What could be the problem?? I was suspecting the connection but as you say it may not be the issue
It could be that contacts have become welded together, or some other failure in the mechanism.
Does it cut power at all if you turn the adjuster to a lower temperature? Or do you hear a faint 'click' when you adjust it back and forth?
If not, best to replace it.
 
It could be that contacts have become welded together, or some other failure in the mechanism.
Does it cut power at all if you turn the adjuster to a lower temperature? Or do you hear a faint 'click' when you adjust it back and forth?
If not, best to replace it.
it cuts when I reduce to less than 30
 
it cuts when I reduce to less than 30
OK - I just need to clarify:
Are you doing this test with the thermostat at ambient temperature, or is it in a hot tank?
If the former, I think you are using an incorrect terminal on the thermostat - using the normally open contact rather than the normally closed.
If your thermostat has a changeover switch like the right hand one in the diagram in post #3, sounds like you have one of your wires on terminal 2 instead of terminal 1.
 

Reply to IMIT TWIN THERMOSTAT (LONG PROBE) Wiring diagram in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All I have been asked to supply a minor works certificate on a smart thermostat upgrade. Would I just test the dedicated circuit from the CU...
Replies
3
Views
319
Hi everyone just looking for some advice before buying stuff not planning on carrying out this work myself will get someone who knows what their...
Replies
2
Views
433
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
712
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
477
Hi - we have an inline heater for a vent system that appears to always be on. I believe the electrician may have wired it incorrectly with only a...
Replies
3
Views
712

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock