Discuss Immersion timers keep failing in the UK Electrical Forum area at ElectriciansForums.net

Subby

-
Reaction score
14
Hi all .
Have been to change an immersion timer for a Santon premier to210e invented cylinder.
This cylinder has a 3kw immersion element (240v)
I have fitted two different timers to replace the original but they have both failed after a few days of operating.
After a few days u no longer get 240v at the switched live terminal in the timer when the timer is calling for heat. This happened to both the timers I fitted (both 16A load rating) one mechanical from the electric merchants, one lap digital one from screwfix.
Why are the timers failing? The element works fine when I link out the timer. Thanks in advance.
 
Thanks for reading my question . What would cause these crap timers to fail in this way? The electrical merchant assured me the one he sold me was the best quality one he had (T104-c)
 
have you checked the supply from fused spur / double pole switch make sure no loose connections ect? same with immersion have you IR tested the element & made sure connections not burnt out & secure?
 
I cant see loose connections causing the internals on the timers to fail, you'd see evidence of that with charred connections.
It's part of life now going back and changing rubbish gear, possibly several times. I had a run of timeguard timers which failed resulting in 3 return visits for FA. Also had a number of 105va LV trannies fail on one particular downlight. 4 return visits and the last one has now been in for 3 years and still going.
 
I cant see loose connections causing the internals on the timers to fail, you'd see evidence of that with charred connections.
It's part of life now going back and changing rubbish gear, possibly several times. I had a run of timeguard timers which failed resulting in 3 return visits for FA. Also had a number of 105va LV trannies fail on one particular downlight. 4 return visits and the last one has now been in for 3 years and still going.
not the internals of the timer, the supply to the timer if loose could be causing more current draw through the unit. just a thought
 
Test the element including a load test.
Yea do this, had one once that was all split open and part of the element was touching the metal sheath so it was drawing more current than it should, but nothing excessive, around 15.5A IIRC no RCD on circuit. That one ----ed the timer which was the reason for the callout.
Any time I do any work on an immersion heater I always carry out an insulation resistance test, current test with clamp meter and earth fault loop impedance test.
 
Thanks. I know it seems that the timers I bought were of low quality but it seems too much of a Co incidence that 3 have gone in the space of a couple of weeks.
Will carry out the tests you mentioned thanks
 
if your water has a high calcium carbonate content (limescale)be a good idea to fit a stainless element.
 

Reply to Immersion timers keep failing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
We have this type of "mechanical" timer switch to control our central heating, which is Potterton combi boiler. The switch keeps failing after 2-3...
Replies
1
Views
1K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
439
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock