Discuss Immitation cable degrading without signs? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
186
Hiya.

For anyone interested in domestic fault finding I had a funny one today...

Customer complained about her bs 3871 popout kept popping on her downstairs and basement sockets so I went round, did my testing and found the circuit was failing the IR tests (I will pass on telling you about the hour long conversations with the senile pensioner customers, where the ground was retrodden more than an army barracks parade ground...).

So... as usual, I split the ring at the believed half way point - to discover both legs were failing the IR test. Ok, not the first time I have had multiple faults on a job...

So... I removed all accessories and tested at each point resulting in fails at 1 leg at lounge socket, 1 leg at a dining room socket next to it, and both legs at a socket next to an electric fire place in the basement directly below. I then deduced whoever fitted out the basement obviously split the cable between the lounge and dining to extend it down to this basement socket and back. All I needed to do now was find the connections (which I'd have expected to be below the lounge/dinging sockets).

So... I ended up cutting 7 holes in the ceiling to find the terminal boxes :grimacing:. They were nowhere near any of the sockets (I couldn't pull the floor up - before you ask). The cables, it would transpire, run from the basement socket, behind the fireplace (with connection teminals enroute in the fire place), through the wall to the other side (which is a utility room), up the wall behind dot & dab where it's worth pointing out they had no protection, no rcd, not in a zone... In fact they were mm away from a picture nail. and then across the ceiling under joists to the terminal boxes 3 feet away from the wall.

IMG_20200827_152914_LI.jpg
basement socket right hand side of fireplace going left and then through the wall to 2b.
IMG_20200827_152927_LI (2).jpg
2b) where they come through wall. 3) terminal boxes. 4) dining room socket above. 5) lounge socket above.

Now the interesting thing is these newer cables were only about 3-5 years old (hard to tell cos the customer got confused as to when it was done) but showed no sign of damage. I managed to pull out one bit between the fireplace and the basement socket, meggered it at 0.17, then opened the cable up to find no damage what so ever. I can only conclude it is immitation black market cable which has let condensation penetrate the insulation making it useless. I would be interested if anyone else has come across this?

It confused me how after splitting the ring I got bad readings from both legs. It was nice to realise I wasn't going crazy o_O... Although the customers made up for that in spades :tearsofjoy:
 
Have you kept sections of the removed cable?

The folk here might want to try and find out its origin, etc, as that is clearly a serious safety risk and they can't be the only household impacted:
 
I too would be interested to see some, especially the markings on it. There have been products insulated with unsuitable / contaminated material that is partially conductive. On the basis of the poor installation method it might not have been tested on completion.

Did you find the cause of the MCB tripping? You mention a reading of '0.17' which I am guessing is megohms. This length of cable would dissipate 0.3W of heat when subjected to 230V. If the resistivity was uniform throughout the material that would probably go unnoticed, but if there are small hotspots amongst generally insulative material, they could reach a high enough temperature to carbonise and enter a runaway condition. Pics of the actual short-circuit would be interesting.

Obviously if you meant 0.17 ohms, that's the short circuit and the only conceivable causes are the conductors touching or a piece of metal embedded in the insulation. (Always state the units, grrr.)
 
i like ohms. they transcend all sysyems whether you work in cgs (centipedes/grams/seconds); MKS (meters /kellogs/seconds) or YTW (yards /tons/weeks) ohms are still ohms.
 
Have you kept sections of the removed cable?

The folk here might want to try and find out its origin, etc, as that is clearly a serious safety risk and they can't be the only household impacted:

Hi.
I managed to pull & keep the bit between the fireplace and socket which I opened up (see below). I have left the rest in place for now as it is embedded in walls etc. There are no markings on this section at least and the primary and outer insulation is fully intact with absolutely no signs of damage. If you want me to post some to you I can do.

There is no sign of moisture in the basement at this time (although they do have a small humidifier on!) I couldn't see any building insulation in the walls/ceiling either which may degrade it. There is the small electrical fire of course which the cable ran a couple of inches behind (with no insulation between). This is where I found the terminal connectors. Not really any signs of thermal damage although it obviously wouldn't do it much good.

Sorry Lucien, It was a long day. I did indeed mean 0.17 megohms on the IR test

I am concerned as there is more of this cable (I assume it's the same cable) in the basement and although I tested it ok that doesn't mean it could be a future hazard.

as an afterthought (I should have done it at the time - Damn it!!) I have just done insulation tests on both the live and neutral, individually, between the conductors and their insulation to get 999. Which is a bit perplexing and I can only assume they have dried out since I removed it??

IMG_20200828_191715.jpg
 
Last edited:
What exactly are you testing this time to get the high reading?
 
What exactly are you testing this time to get the high reading?
Insulation test at 500v between the actual live conductor and the inner insulation around the conductor. I did it at several points on the insulation along the cable length (3ft). If it failed before between live and earth (0.17) then I expected it to fail under this test but it hasn't. That could be because I am only testing 5mm surface area at a time (width of my test clip) at several positions along the length as apposed to testing the whole length surface area or it could be it has dried out. I can't think of another explanation

IMG_20200828_203521.jpg
 
It is perplexing.

An IR value of 0.17M won't fire a 30mA RCD, let along a MCB, but it clearly says that circuit is seriously wrong. If you measured it on a removed section (i.e. isolated) then it has to be the cable, but I would be most surprised even with some damp to get anything that low. Unless the PVC has some other issues, which is not unbelievable :(
 
It is perplexing.

An IR value of 0.17M won't fire a 30mA RCD, let along a MCB, but it clearly says that circuit is seriously wrong. If you measured it on a removed section (i.e. isolated) then it has to be the cable, but I would be most surprised even with some damp to get anything that low. Unless the PVC has some other issues, which is not unbelievable :(
I should point out, the circuit was energised and working when I got there. The customer had been complaining it kept tripping though (about several hours beforehand and the day before etc.). I checked through the usual suspects (kettle, toaster etc) and couldn't find any issues. I was unable to get much info from the customers unfortunately. I did start a few arguements between them, on what they were doing at the time etc, though :tearsofjoy:

Old Wylex board btw. No RCD
 
Putting a clip onto the insulation will barely contact a square mm, whereas if the sheath and insulation are both conductive, there could have been thousands of times that area between L & CPC when the cable was intact, so the measurement is not comparable.

Place the insulated conductor in a tray or jug with the ends overhanging the sides. Cover it with slightly salt water and test between the water and one of the exposed ends. The water will make intimate contact with the entire surface area, as the sheath would have done. Within the duration of the test, the insulation should not absorb enough water to significantly affect its resistivity.
 
Putting a clip onto the insulation will barely contact a square mm, whereas if the sheath and insulation are both conductive, there could have been thousands of times that area between L & CPC when the cable was intact, so the measurement is not comparable.

Place the insulated conductor in a tray or jug with the ends overhanging the sides. Cover it with slightly salt water and test between the water and one of the exposed ends. The water will make intimate contact with the entire surface area, as the sheath would have done. Within the duration of the test, the insulation should not absorb enough water to significantly affect its resistivity.

WOW!! With immediate effect as soon as I put the cable in the water. Note: I also tested some of my legit cable, just to empaphise the legitimacy of the test (and my curiosity) which passed with >999.
I will remember this one... And must contact the customer to suggest it being replaced. I will suggest they contact whoever installed it and demand they see it good at no charge.
 
Last edited:
It might be partially conductive, or it might have pinholes or porosity. I was going to say you should do a control test with some normal cable and it's good that this came up off-scale. It's always possible for moisture on the surface to form a conductive path to the exposed conductor. In a genuine lab test, a guard electrode would fitted onto any surface that could carry leakage and my high-range insulation testers have guard terminals. A guard terminal is connected to the same potential source as the measurement terminal that it guards, but bypasses the meter itself, so that the surface leakage is collected without contributing to the measurement. No measurable leakage occurs between the measurement terminal and the guard because they are at effectively the same potential.

When you have time, send me a bit, preferably the whole cable if you go back to do remedials. I'm working flat out at the mo, 7 long days per week, will be going round the clock even on the bank holiday. But when time permits, I'd like to have a play and find out what is up with it.
 

Reply to Immitation cable degrading without signs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
630
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock