Discuss In-Rush Current on Pressure Washer in the Electrical Appliances Forum area at ElectriciansForums.net

S

SKY

Have an install where a professional pressure washer is popping the fuse on start up.

The circuit is a 16a Radial from board to garage approx 15m long all fed by 2.5mm.

The washer is a commercial 1 phase unit and has the auto start and stop once the trigger is pressed as soon as the owner starts the machine the mcb pops out.

Washer is 2.8kw so 12a - the fluke says its pulling 11.35 when running but the inrush current is nearly 50 amps for a split second.

Will changing the MCB to a C curve 20amp cope for the split second (board is crabtree starbreaker so c curve is all I can go upto).
It works perfectly when plugged into a 32A ring.
 
a 20A C type will probably get you out of trouble here.
 
Have an install where a professional pressure washer is popping the fuse on start up.

The circuit is a 16a Radial from board to garage approx 15m long all fed by 2.5mm.

The washer is a commercial 1 phase unit and has the auto start and stop once the trigger is pressed as soon as the owner starts the machine the mcb pops out.

Washer is 2.8kw so 12a - the fluke says its pulling 11.35 when running but the inrush current is nearly 50 amps for a split second.

Will changing the MCB to a C curve 20amp cope for the split second (board is crabtree starbreaker so c curve is all I can go upto).
It works perfectly when plugged into a 32A ring.

Your opening post is confusing. If it's tripping a b curve MCB then a c curve would be the remedy. If it's blowing a fuse then it's possibly a fault with the appliance, fuses are generally a lot more forgiving than an MCB.
 
Popping the fuse is a generic term in my book and 99% of the sparks I work with will understand.
also all uk pros would have understood the setup as I said the board was Crabtree star breaker.
Thanks for the advice.
 
The pressure washers motor will have a KW RATING unless this is what you have provided and at 230v a standard 2.2kw motor would require a 40amp type b or c to eliminate nuisance tripping 100% also a 25(d) would do the same job, what is the rating of the motor itself... Note you cant use basic ohms law what converting motor KW ratings into amps.

If its supplied with a 13amp plug top then step will have been taken by the manufacturer to limit the inrush to allow plugging in to a ring main possibly but anything below may trip regardless of type.
 
Last edited:

Reply to In-Rush Current on Pressure Washer in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi all. Talented amateur here, stage electrician at school 1971 - 74 and have done much DIY electrical work iover the years, including central...
Replies
16
Views
4K
hi im new to all this and wonder if you guys could help me out. I am trying to repair a pressure washer at work basicly it keeps blowing a 13amp...
Replies
7
Views
37K
BernieKaval
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock