Discuss Individual RCBO in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

T

trebor12345

Hi

I need to check what the electrical requirements (17th addition and Part P) are for RCBO's on a new kitchen extension.

Using the existing house Consumer Unit with one 100Amp 30ma RCBO.

Do all the different new kitchen circuits i.e Ring Main, Cookers (x2), Indiuction Hob, Lighting, Smoke/Fire Detectors, etc require their own individual RCBO? Or is one single RCBO (30ma 100Amp) supplying all circuits acceptable?

Thank you for your replies.
 
You need 30ma RCD protection so an 100A RCD or RCBO achieves that but its not ideal as you risk nuisance tripping and everything going down.
The smoke fire detectors shouldn't be losing power qhen the main earth leakage protection trips.
Individual RCBOs is a better solution.
 
I would explain the issues facing an installation with a single upfront rcd plunging into complete darkness......

And then see if they would agree to a cu upgrade and then go for RCBO's.....

Don't forget about making sure that earning and bonding are up to scratch.
 
Without seeing the unit its hard to confirm but it sounds like that it is. Loads of houses wired like that but its not a good system.
What type of earthing is it?
 
I would explain the issues facing an installation with a single upfront rcd plunging into complete darkness......

And then see if they would agree to a cu upgrade and then go for RCBO's.....

Don't forget about making sure that earning and bonding are up to scratch.

It's always about the money with you !! :D
 
Agree with the others here, can you actually get a 100A rcbo. Like already said can you post a picture.
 
I was just going to say he may have an Rccb in his head
 
An rcbo is a combination of an mcb and an rcd so offers overcurrent and additional rcd protection. Your rcd only gives the rcd protection.
 
So the device in the picture is a RCD which provides protection against any earth leakage, is that right? So the individual breakers (one show in the right of the picture) provides the overcurrent protection, is that right?
 
Looks like a split load board so the rcd only protects some of the circuits, probably the power. I must say the rcd looks a bit wonky like it isn't fitted correctly.
 
Hi

I need to check what the electrical requirements (17th addition and Part P) are for RCBO's on a new kitchen extension.

Using the existing house Consumer Unit with one 100Amp 30ma RCBO.

Do all the different new kitchen circuits i.e Ring Main, Cookers (x2), Indiuction Hob, Lighting, Smoke/Fire Detectors, etc require their own individual RCBO? Or is one single RCBO (30ma 100Amp) supplying all circuits acceptable?

Thank you for your replies.

So that we know how to pitch replies, and since your profile says that you have no electrical qualifications, are you an electrician?
 
Yes thats correct. The 100A raining is just the max current its designed to work at. But it won't trip at 100A it woukd most likely just overheat and or fail to release correctly.
Also RCBOs normally have their own neutral fly lead.
 

Reply to Individual RCBO in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
737
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
325
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock