Discuss Induced voltage. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi
Just replaced a bathroom extractor fan. I didn't alter any wiring.
Both old & new have live & switched live. Trouble is, once activated, the fan won't turn off.
Vent axia say there's an induced voltage. Not enough to switch fan but enough to keep it running. Sure enough, there seems to be 37v.
They say to run in a new, seperate switch live.
Any advice/thoughts welcome
 
Firstly I’d double check (presume you have) that the cores are actually what you’d expect I.e. brown -line
Black -switched line & grey - neutral. Presuming these are correct and when tested the 240 does actually drop off to 37v when light turned off and timer over run has stopped. Then I suppose it could be induced voltage🤔
If it is then maybe try swapping the neutral and switched line cores around (obviously at both ends and mark accordingly) possible having the neutral between the line and switch line may eliminate the induced voltage. Never tried if just something that popped into my head. Hmmmmmm 🤔🤔🤔
 
It is unlikely that "induced voltage" is able to actually run anything, sick a voltage tester that draws a couple of mA for LEDs on it and it collapses to near-zero.

As @Bsharp suggested, check the permanent and switched lives are as expected. Also some fans just have problems with timers and go bad, if nothing else explains things that is a possible reason.
 
It is unlikely that "induced voltage" is able to actually run anything, sick a voltage tester that draws a couple of mA for LEDs on it and it collapses to near-zero.

As @Bsharp suggested, check the permanent and switched lives are as expected. Also some fans just have problems with timers and go bad, if nothing else explains things that is a possible reason.
Yer reckon your correct, never seen a fan running via induced voltage only ever had dimly lit LEDs. But with fans “always running” as you say timers can go bad also when waiting for an over run to stop this can seem like an endless amount of time.
 

Reply to Induced voltage. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
806
HI There, I would be grateful if you could help me, I have a very long duct between the bathroom and extractor outlet vent and for sometime, the...
Replies
3
Views
1K
I've installed a replacement bathroom extractor fan. Pic on the left is the old one. Pic on right is the new one. Wired the same way but the fan...
Replies
4
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock