Discuss Induction hob for preexisting 4mm T+E in the UK Electrical Forum area at ElectriciansForums.net

Jackster

DIY
Reaction score
6
I have been told by a local spark that one can not run an induction hob on a 4mm T+E.

From my understanding, most induction hobs are 7-8kW and "require" 6-10mm T+E but our housebuilder only put 4mm because they are cheap.
Or maybe I am cheap for not coughing up £500 for a £150 induction hob "upgrade" when we bought...

Anyway, there is a 4mm T+E installed and I don't want my local spark coming and running new cable in my new build house. CBA with the mess.

I am aware of the 13amp ones but after using a full-power one at my old house, doubt a 13amp one will suffice my expectations.

So are there any mid-powered induction hobs models out there that can run on 4mm?

Note that a 2kW oven will have to be moved onto the kitchen circuit if I get this done.
We have a microwave, dishwasher, washing machine, kettle and Foodi Ninja (2kW pressure-cooker/grill machine).
All these devices won't be on at the same time so this should be okay on the kitchen circuit? B32 breaker in the CU.

Also, if 4mm should not be used on 32amp equipment. Why did my house builder put the 4mm T+E on a B32 breaker?
 
Also, if 4mm should not be used on 32amp equipment. Why did my house builder put the 4mm T+E on a B32 breaker?
4 mm is fine, (installation conditions permitting) On a 32a breaker, depending on installation method 4 mm will carry a max 46a (not with a 32a ocpd obviously)....although to be honest I think I’d have paid for the larger cable at build stage to future proof and save all this grief but good luck with it ?
 
I have been told by a local spark that one can not run an induction hob on a 4mm T+E.

Note that a 2kW oven will have to be moved onto the kitchen circuit if I get this done.

Also, if 4mm should not be used on 32amp equipment. Why did my house builder put the 4mm T+E on a B32 breaker?

Did the local spark support this statement with any reference to the wiring regulations?

A 2kW oven shouldn't be put on the socket circuit, it's not strictly prohibited but strongly advised against.

Depending on the installation conditions and cable calculations 4mm could be used for a 32A circuit. Was this actually installed by the builder, or was it an electrician working for the builder?
Do you have an electrical installation certificate for the installation?
 
From my understanding, most induction hobs are 7-8kW and "require" 6-10mm T+E but our housebuilder only put 4mm because they are cheap.
Or maybe I am cheap for not coughing up £500 for a £150 induction hob "upgrade" when we bought...
Most manufacturers put in a cable to the rating of the hob plus tells inthe installation book what rating of the cable to use.
 
A lot of these hobs come with a flex cable attached to connect to the cooker outlet, and they’re lucky if it’s 4mm.

yes, I know, the type of flex has a different ccc to t&e

the circuit should have been 6mm to begin with. Majority of people have seperate hob and oven now, and the two could be doubled up, rather than oven on rfc with every other high powered kitchen appliance.
 
A 25A MCB can get you out of trouble with 4.0mm as a couple of methods give an Iz between 25 and 32A.
 
Did the local spark support this statement with any reference to the wiring regulations?

A 2kW oven shouldn't be put on the socket circuit, it's not strictly prohibited but strongly advised against.

Depending on the installation conditions and cable calculations 4mm could be used for a 32A circuit. Was this actually installed by the builder, or was it an electrician working for the builder?
Do you have an electrical installation certificate for the installation?
I know you're a stickler for precision Dave so I'll correct you a little, of course I fully expect you to point out my unseen error :) .
Cookers/ovens/hobs with a rated power exceeding 2kW on their own dedicated radial circuit (Appendix 15, note (iii)). So a 2kW cooker would be deemed OK on a socket circuit, a 2.01kW cooker would however require a dedicated circuit.
 
I know you're a stickler for precision Dave so I'll correct you a little, of course I fully expect you to point out my unseen error :) .
Cookers/ovens/hobs with a rated power exceeding 2kW on their own dedicated radial circuit (Appendix 15, note (iii)). So a 2kW cooker would be deemed OK on a socket circuit, a 2.01kW cooker would however require a dedicated circuit.
oops, davesparks and hippyhappy---- handbags at dawn.
 
Interesting info. Thanks for the replies, everyone.

So it is pretty much safe to say the 4mm T+E can handle the induction hob, and the over can go on the kitchen circuit.
Though ideally there should be a 6mm T+E with both on that.

Best bet would be a 6kW induction hob to be on the safe side?
 
I know you're a stickler for precision Dave so I'll correct you a little, of course I fully expect you to point out my unseen error :) .
Cookers/ovens/hobs with a rated power exceeding 2kW on their own dedicated radial circuit (Appendix 15, note (iii)). So a 2kW cooker would be deemed OK on a socket circuit, a 2.01kW cooker would however require a dedicated circuit.

That is a good point, it is indeed on the borderline.

I guess it's going to come down to whether the power rating is just the element or if it includes the electronic clock and the lamp in the oven :tearsofjoy:
[automerge]1594386885[/automerge]
So it is pretty much safe to say the 4mm T+E can handle the induction hob, and the over can go on the kitchen circuit.

Maybe, maybe not, we haven't seen the actual installation to be able to make that decision.
 

Reply to Induction hob for preexisting 4mm T+E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
822
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi, Just looking for a bit of advice here. I am considering swapping my existing 4 burner gas hob for a Bosch induction one. I am not proposing...
Replies
10
Views
5K
Howdy experts, I normally run 6mm T+E for cooker circuits, housing authority spec. I'm changing my gas inbuilt double oven and hob for...
Replies
9
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock