Doh, I just double-checked the oven and it is 2,075 watts not 1900 watts.
Think I was looking at another oven a few weeks ago trying to get a better one.

Maybe, maybe not, we haven't seen the actual installation to be able to make that decision.

Ah...

It goes from the understands cupboard to the kitchen in the ceiling cavity.
Don't believe there is any insulation up there. And it should be clipped?
 
Doh, I just double-checked the oven and it is 2,075 watts not 1900 watts.
Think I was looking at another oven a few weeks ago trying to get a better one.



Ah...

It goes from the understands cupboard to the kitchen in the ceiling cavity.
Don't believe there is any insulation up there. And it should be clipped?
bear in mind yhat thatis the total ratingof the oven. youprobably won't be able to use oven and grill elements together, and even so, it's under 9Amps. can'tseea problem on the socket ring unles you have a washing macine and tumble dryer on at same time as oven. anyway, we all plug a 3kW kettle in and nobody bats an eyelid.
 
Its been done for decades, everybody knows a dedicated 32amp cooker circuit should be run in 6mm minimum.
@7029 dave , I would install 32A on 6mm too, just because it's always done that way. But I often wonder why? I could see 6mm being necessary for voltage drop concerns, or if using rewireable fuses. In the absence of these, and assuming method C, why wouldn't a 4mm conductor suffice?
 
6 mm for a cooker circuit is a throw back to the older 3036 fuses, where 6mm on a 30 amp fuse was the norm as it dealt with the issue of the fusing factor of the 3036 fuses being 2 rather than 1.45 , I2 < 1.45 Iz.
So a 6mm for a cooker circuit has just been recycled down the line without any thought on actual design.
Considering that a 15kw load is fine for a 32 amp mcb with diversity taken into account, 4mm is quite adequate for a cooker circuit, obviously if the calculations allow it, the same as any other selected conductor.
 
Its been done for decades, everybody knows a dedicated 32amp cooker circuit should be run in 6mm minimum.

But everybody knows that a 32A socket radial should be 4mm, so what's the difference? Same size OCPD, same calculation, different cable size?

'everybody knows' isn't always correct, it can just mean that a lot of people are wrong.

6mm is traditionally used for cooker supplies yes, but that is out of tradition, not calculations. It harks back to the imperial cable sizes where the size used for a 32A radial was nearer to 6mm and so people just started using 6mm.
 
@7029 dave , I would install 32A on 6mm too, just because it's always done that way. But I often wonder why? I could see 6mm being necessary for voltage drop concerns, or if using rewireable fuses. In the absence of these, and assuming method C, why wouldn't a 4mm conductor suffice?
The OP stated it is a new build so method C is out the window we have been told that, which will reduce the CCC thats why 4mm wont suffice.
 
But everybody knows that a 32A socket radial should be 4mm, so what's the difference? Same size OCPD, same calculation, different cable size?

'everybody knows' isn't always correct, it can just mean that a lot of people are wrong.

6mm is traditionally used for cooker supplies yes, but that is out of tradition, not calculations. It harks back to the imperial cable sizes where the size used for a 32A radial was nearer to 6mm and so people just started using 6mm.
I would use the term common sense other than tradition, out of interest given the info we have, what size cable would you select.?
[automerge]1594462859[/automerge]
Why is method C out the window?
Our company do new builds, method C is common to a lot of the circuits installed
My understanding is that is a surface install.
 

Reply to Induction hob for preexisting 4mm T+E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
822
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi, Just looking for a bit of advice here. I am considering swapping my existing 4 burner gas hob for a Bosch induction one. I am not proposing...
Replies
10
Views
5K
Howdy experts, I normally run 6mm T+E for cooker circuits, housing authority spec. I'm changing my gas inbuilt double oven and hob for...
Replies
9
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock