ive been investigating an intermittent fault that causes the bottom rcd of a 20 way dual rcd cu to trip approx every 8/10 days. (Really annoying fault to trace)..
i used a mili amp clamp meter today to measure the leakage to earth from the bottom row and got a reading of near to 30ma (strange as the rcd trips on ramp test at about 25ish)
however when I started to isolate circuits to see if I could see if a circuit was excessively leaking to earth nothing much seemed to change on the metre reading... I then started to disconnect the cpcs one at a time to see if I could cause the reading to drop...
when I disconnected the cpc for the induction hob circuit (40 amp 10 mm feed) I saw an arc from the cpc to the earth terminal bar (I know you shouldn't disconnect cpc when live but scratching my head here!) I then went to put the cpc back in and as I touched the copper to straighten it I received one of the finest belts in my history as a spark!!! I then carried out IR test on my feed and everything was clear.. I then removed the isolator under the hob and tested here ...and as I clamped my leads on my cpc and then the earth from the hob my meter showed 192 v and 50 hz??? ( meter was in series so in theory I shouldn't of had a reading?) is there some serious capacitors inside the hob? And if so why when I splashed the cpc didn't the arc stop it was continuous? Hope this makes sense any ideas greatly appreciated!!
thanks in advance

jamie
 
Welcome to the forum.

Are you saying that if you clamp round the L & N feeding the bottom RCD and then turn off the MCB supplying the induction hob, that the differential current measured doesn't change significantly?
 
Welcome to the forum.

Are you saying that if you clamp round the L & N feeding the bottom RCD and then turn off the MCB supplying the induction hob, that the differential current measured doesn't change significantly?

Sorry...I'm using a mili amp clamp metre around the earth of the install
 
Sorry...I'm using a mili amp clamp metre around the earth of the install

If you're trying to look at why an RCD is tripping, you need to be measuring the differential current that the RCD itself is seeing. Clamping an earth conductor is likely to give all sorts of odd readings, depending on the earthing system, parallel paths, etc.

What is the earthing system?
 
EMI filters in induction hobs can cause high leakage due to capacitors from lives to CPC, this is normal. Whether it is too high will be determined by test as per Handysparks above. Capacitors do not influence IR test as that is DC.

E2A: Don't energise a circuit with its CPC disconnected. There is always a safer, alternative way to test it, whatever might be wrong with it.
 
Thanks for the advice....
asuming that the induction hob is (normal) and its some form of internal strange going ons how would you go about trying to locate the fault that intermittently takes out the rcd?
i was thinking of moving a circuit onto a rcbo above? To try and reduce the leakage on the bottom row of circuits?
 
might be an idea. put the hob on it's own RCBO, or, as a temp. measure, a non-RCD protected MCB. if the hob is the problem, then you'll have it verified after a while with no RCD trips.
 

Reply to Induction hob possible fault! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
About 5 years ago during a full refurb on my house I re-wired the property myself (old aluminium wiring) in line with 17th edition. I had it all...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
404

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock