I need a bit of advice with inrush current on lighting. I have been reading through the IET circuit design guide & i cannot seem to find any answers to my questions.
1. Should the cable be rated at the running current or the inrush current? I was taught at college that the cable should be rated at the inrush current including any accessories, such as switches. The inrush should be taken as 1.8 x the running current.
But inrush current on certain lighting can be many times higher that 1.8.
It would appreciated if someone could point me in the right direction.

Cheers
 
cables should be rated to thre flc of the load. the inrush is onlt for a few mSec, and the cable will withstand the overload for such a short time. however, you may need to use a c curve breaker to cope with the inrush.
 
As per what Tel said, although circuits are primarily designed around running currents you may need to accommodate inrush currents in your design with regard to volt-drop and the curve of the OCPD etc.
 
It's also worth pointing out that with certain types of lighting the start up current could be as long as several minutes so don't class this as 'in-rush' current because it isn't.
 
Your confusion is coming from the need for switching to be rated for the inductive nature of the load, this means its can cope with the large spike as you turn the lights off, in the domestic realm you really don't come across any real design issues with lighting etc unless you have an excessive amount of inductive lighting.

When in commercial and Industrial the ball game can change greatly and you may need to use contactors for effective switching of the larger lighting circuits found, the cable, switches etc flc is compensated when you use the 1.8 factor for inductive lighting in your calcs, what will be your biggest issue on larger circuits is nuisance tripping of incorrectly spec'd mcb's.... manufacturers of the circuit breakers will provide you with a lamps per amp chart that gives the max no' of various inductive lighting types and this is the first step before any calculation is done as this with be key to how the circuits are divided and spread across the consumer unit without the risk of nuisance tripping.

Now inductive motors is a whole new ball game but thats for another thread.
 
Thank you darkwood, that's really interesting regarding the circuit breaker charts. So the 1.8 multiplier should be used for inductive lighting loads and this will be the flc to which switches etc are rated.
 

Reply to Inrush currents in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
751
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs). 6A breaker in Garage consumer...
Replies
16
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
537
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
442

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock