What is the definition of premises with regards to where the main bonding should go?

I live in a 4 stroy mid terrace house. The road is level with 1st floor. There is a small sun-con courtyard with a path/bridge from the road to the front door on the 1st floor. The services run under the path. The water stoptap is approx half way along the water pipe. The house side of the stoptap is where the current 6mm earth bond is (needs up'd to 10mm) The CB is the other side of the wall ie in the house. Inside the house the water pipe has been plastered over.
So do I need to dig the pipe out and earth once it is in the house or is replacing the 6mm with 10 under the path acceptable?
 
What earthing have you got and what exactly are you doing as if it's tns with 60a mainfuse 6mm mpbc is acceptable.
 
Its TNS, not sure of fuse size as no indication, so would have to pull out to check. The earth coming off the outside of the incoming cable looks like its only 2.5mm csa with no insulation. From the earth block I have 10mm to DB and 6mm to water and gas incomers.
 
you need to bond the services water gas oil etc where it comes into the house within 600 mm and before the first joint , main earth to DB needs to be 16mm , do a Ze test to confirm a connection has been made to the outer sheath TNS max is 0.8 ,TNCS 0.35
 
Last edited by a moderator:
The water bond should go to the point of entry to the property or as near as practical
If its buried where it comes in, I would bond at the nearest position the pipe is exposed
 

Reply to Inside or out? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
902
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock