Discuss installing a shower in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Hi,

have a shower connect up, the run to CU is maybe 8 metres, (3036's) but the CU is in a meter cupboard outside.

There is no space to put a rcd unit inside, and not enough room for a henley block..

was going to get a plug in 40a wylex mcb as there is an existing spare way in the CU, go through the wall (the room with a separate shower room is directly behind the existing board)

and use a small shower CU with RCD to connect this, Ideally it would have 16mm tails from a henley block but i cant do that with space constraints...

Is it pointless to go from original CU, 40a plug in wylex, into rcd unit with a 40a 60898? i am assuming the plug in wylex's have the same disconection times?
 
If you're going through the wall with the cable from the old board won't it need RCD protection?
 
it'll need a RCD anyway, special location , section 7, BGB. and it doesn't need RCD for going through a wall, only cables buried up/down wall < 2" deep without blah, blah. blah.
 
shower is 8.5kw,

yes, i suspected that the 20cm distance through the wall would bring up this issue...
but it can be mechanically protected by a short length of conduit..

i want to get the rcd in before the wall, but there really is no space, and without changing the entire CU there is no way of implementing that.

any suggestions?
 
it's the shower that's in the location. and you don't need to fit RCD to cable passing through a wall.
 
hmm, maybe i haven't explained this right,

outside CU, plug in 40a wylex (60898? not sure) to fit 3036 slot. hole to opposite side of wall, directly into new CU with RCD and 40a 60898, to feed shower.

but the 40a MCB in the shower CU may be pointless, but i am unsure if the plug in wylex fuses operate the same as 60898's
 
the later plu-in MCBs are 60898. it's the old push button ones are 3871. just come off your 40A wylex MCB ( and N & E, of course ) and fit RCD in enclosure other side of wall. you don't want 2 MCBs in series. no discrimination.
 
They do.

From what your asking you can just wire the shower into the spare way and put the push MCB in place, it'll be fine.

- - - Updated - - -

As long as the cables sufficiently meet the requirements for a non RCD circuit.
 
They do.

From what your asking you can just wire the shower into the spare way and put the push MCB in place, it'll be fine.

- - - Updated - - -

As long as the cables sufficiently meet the requirements for a non RCD circuit.

the shower itself must be RCD protected. 701.411.3.3
 
I did think as much, hence my idea for a local RCD, the RCD doesn’t have to be in the board but it does have to be before the circuit enters the zone, unless the whole cable require protection due to the installation characteristics, would you say?
 
ok, thanks.. yeah it was the push button ones i was thinking perhaps they were similar to the new plug in ones.

and cheers for the advice, and of course the shower needs rcd protection, hence this entire post.

nice one, feel free to talk amongst yourselves
 

Reply to installing a shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
690
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
845
Hello, DIY'er here looking for some advice. In March 2023 we should be getting 5.5kW of solar PV going on the roof feeding into the current...
Replies
4
Views
1K
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock