Discuss Installing induction hob+electric oven...separate circuits or same? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
New kitchen - induction hob at 7.4kW (32amp) and oven at 3.6kW (16amp) max ratings. Existing outlets are:
1. 45amp fused cooker circuit
2. fused socket off ring main (32A fuse)

Can both oven and hob be connected off the one 45amp cooker circuit? That's right up to the maximum.

Or can the oven be connected to the ring main?

Or does the oven require its own circuit - that would be an extra installation and need rewiring to the fuse box.
 
Hi - I'm not a qualified electrician but I build a lot of electronics, so familiar with calculations and wiring stuff up. What I want here is a correct plan so I know what the installation is likely to be and how it affects the layout of the rooms and units.

I've read a lot of posts on this already, and you might be surprised how much they vary. For example, even electricians say they're fine with twin and earth, where cooker manufacturers always specify heat resistant cable. I already bought Butyl coated 6mm cable for the induction hob, which meets the standards of heat resistance.

I'm hoping this forum can offer me a more definitive answer to this fairly common question.
 
There are some variables, and sitting from here its to easy to take things for granted. OP there is a factor called diversity that can be applied to these circuits & appliances, but there is also a recommendation about ovens/hobs etc, with a load of more than 2kw having their own radial.

The first question would be exactly what does your 45amp fused cooker circuit consist of?
 
The first question would be exactly what does your 45amp fused cooker circuit consist of?
Absoluutely. 45Amp is quite an unusual rating for a circuit (not unknown, but unusual). What makes you think it is 45 amps?

So, need to know
1. the size of the fuse or MCB in the consumer unit that protects this "cooker" circuit
2. the size of the cable

Two other items

That's right up to the maximum.
Well no it isn't/ When calculating the maximum demand for circuits we use a technique called 'diversity'. This allows us to reduce the assumed max current that a domestic oven etc will use in practice. this is based on the fact that everything in an oven/hob etc is thermostatically controlled so that, statistically, the appliances never pull the quoted maximum current.
There's an interesting article on this at TLC Electrical Supplies - https://www.tlc-direct.co.uk/Book/6.5.2.htm

Or can the oven be connected to the ring main?
Ah, no.

But it is likely that both can go on your existing circuit - depends on your answers to the questions, above...
 
Good points. The 45 amp circuit comes from the fuse box, where there's a 45 amp fuse, into a wall mounted switch with neon (no fuse). The wiring here is 5mm OD overall including insulation - I haven't looked up specifications yet to determine if this is 6mm or 10mm. Should be 10mm, so I hope that's right. The same diameter wiring goes down to what looks like a 45 amp junction box on the wall under the worktop. This is a usual single size junction box, i.e. 850x850mm.

If the supply were split into hob and oven, I'm thinking it would need a larger 3-way junction box. I'm expecting the 5mm OD cable to be 10mm, and from there it would go to a 6mm for hob and 2.5mm for oven. The butyl cable to the hob is 15mm OD including insulation - pretty solid.
 
Send me a photo of that 6mm cable connected to the hob/oven when you're finished, when many are designed (and ask in MI) for 2.5mm. You'll do well to terminate a 6mm cable in to most of the hobs/ovens I've come across.
 
Send me a photo of that 6mm cable connected to the hob/oven when you're finished, when many are designed (and ask in MI) for 2.5mm. You'll do well to terminate a 6mm cable in to most of the hobs/ovens I've come across.

Sigh.... absolutely. This is an AEG hob and while they specify 6mm heat resistant cable it wouldn't surprise me if it's too thick to fit properly, just like you say. Haven't come to that bit yet.
 
Sigh.... absolutely. This is an AEG hob and while they specify 6mm heat resistant cable it wouldn't surprise me if it's too thick to fit properly, just like you say. Haven't come to that bit yet.

OP, not sure how it works, but you would have been better posting in the DIY section. Bit late now.

There's too much guessing (5mm OD cable to be 10mm) to be sure you have a 45amp supply, i.e. 10mm cable. Most cooker radial supplies are 32amp MCB & 6mm 6242y cable. It may be you have a 10mm cable, but the MCB might have been previously upgraded to 45amp, but not the 6mm cable.

Allowing for diversity & installation method, a 32amp supply may be suitable for you appliances, it may not. The heat resistance cable, is only necessary for the final connection to the appliance (if the manufacturer recommends it), and may not have to be 6mm in size, flexible cables have differing ccc to 6242y cables.

In all honesty, you might wish to consider employing an electrician to carry out this work (looks like a kitchen refurb anyway). Otherwise you might have a supply that's too small, or end up installing a larger cable that is unnecessary. If you do end up with a new circuit, this is notifiable to the LBC. And if the any additions/alterations cables are installed in walls, it may require additional protection by RCD. Use an electrician. :)
 
Thanks, Midwest. Evidently the first thing I need to know is what cable is in cooker radial supply. If the OD of the cableing is 5mm, looks like 6mm to me. I've been looking up specifications and the OD of a 10mm earth wire is at least 6.1mm for the earth wire:

20147721 | Prysmian 6491X H07V-R Conduit Cable, 10 mm² CSA, , 750 V Green/Yellow PVC 100m | Prysmian - http://uk.rs-online.com/web/p/conduit-trunking-cable/0381292/

In fact while pos and neg are 5mm OD, the existing earth is a bit less than that. So looks like I can forget running hob and oven off the existing cooker supply, which looks like 32 amp with a 45 amp fuse. But that's OK for the hob at least.

That leaves the oven - 16 amps. There's a mains socket under the worktop with a fused switch above which comes off the ring mains. So the question would be whether - considering diversity - it would be wise to run the oven off that. There's space in the fuse box for one more fuse, and it wouldn't be too disruptive to install another supply to the oven. I just want to know if it's necessary to meet wiring regs.
 
With diversity taken in to account the load comes to roughly 21A. How is the 6mm cable cooker supply installed?

As I was saying above, there are 2 supplies under the worktop

1. Cooker supply, as described, 45 amp fuse in fusebox but looks like 6mm 32 amp supply with a switch and neon above the worktop, so suitable for hob only
2. Fused and switched supply off the ring mains which may or may not be suitable for a 16 amp 3.6kW (max) oven
 
You're talking about the "cooker" supply here? What do you mean by "does the route encounter any insulation"?
How a cable is installed is called the installation method. The installation method is a factor that determines the current carrying capacity of the cable. One of the worst installation methods with regards to current carrying capacity is when the cable is run through or touching insulation. Do you know how your 6mm oven supply is installed so we can get a better picture of the current carrying capacity of the cable to aid further advice?
 

Reply to Installing induction hob+electric oven...separate circuits or same? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
666
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
949
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock