Discuss Installing RCBO-Surge Protector inside Meter Cupboard in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Hi, need your advise please as need to take supply for Electric car charger from the meter cupboard.
This meter cupboard has an isolator and already has Henley blocks from which supply can be drawn to feed the RCBO-SPD device.
I have made a mock up of the intention in the image below (RCBO-SPD & DIN rail).
If we assume there are no DNO issues with placing the RCBO-SPD device inside the meter cupboard, is it okay to do this (or) should this have an enclosure within which the RCBO-SPD device should be placed. Thanks.
Screenshot 2023-05-22 at 13.38.59.png
 
A device with exposed terminals is not advisable in a meter cupboard. The homeowner may open the cabinet to check meter readings. Needs to be in an enclosure really.

I know somebody will say the meter cupboard needs a tool to open it, but that's stretching things a bit.
 
I just typed this so will post it anyway
As a general point you can't just use a DIN rail and devices as you are leaving live parts accessible. Everything in a meter box is generally treated as though it can be left open and ordinary people will be going in there to read meter or even turn off the whole lot.
 
Looks like the inner cores of the SWA disappearing through the side of the box just sitting there. How is the SWA terminated?
If this isn’t a locked enclosure, the reasoning being a normal person can open it to read the meter, then those cores would need covered.

The black could do with some green yellow on it.
 
Looks like the inner cores of the SWA disappearing through the side of the box just sitting there. How is the SWA terminated?
If this isn’t a locked enclosure, the reasoning being a normal person can open it to read the meter, then those cores would need covered.

The black could do with some green yellow on it.
SWA going into the wall and comes out on the other end to the main consumer unit located inside the house.
Good point on the black, will get that dressed with some green-yellow tape. thx
 
This would be in an enclosure I presume? If so then I would be fine fitting it there. If you intend on mounting it directly on din rail and leaving the terminals exposed, I’d say that’s a no no.
 
More specifically about the SWA - how is the armour earthed?

It really should go in to some metal box where a proper gland terminates the armour and allows that to be linked to the main earth.

Already mentioned above is the exposed primary insulation of the SWA cores, at the very least they should be sleeved.
 
I would get rid of the henley's and the isolator and fit a fused connection unit with the swa glanded in properly.


It was destined to be a mess from the start, it looks like they took a hammer to the cabinet rather than a hole cutter.
 
I would get rid of the henley's and the isolator and fit a fused connection unit with the swa glanded in properly.
It was destined to be a mess from the start, it looks like they took a hammer to the cabinet rather than a hole cutter.
Looks like they couldn't decide which side of the cabinet to use for entry.
 
I think the guy has got the message that it's left wanting in several ways.
It would be good if we didn't scare him away.
I'm curious about the circumstances, he may have bitten off too much or he may have been thrown into the deep end without enough help. It's good he's got onto the trainee forum now.
 
Thanks guys, I'm still here - this is the handy work of Bellway developers who built this in 2019. It's been like that since then, no EV charger was provided by Bellway
So if current setup is no good then not sure how it all got inspected and signed off by them.....will post a fuller picture shortly so you can all see the full setup and feedback.
Thanks, really appreciate the comments, helps me understand and gives me pointers to set things right for the long run.
 

Reply to Installing RCBO-Surge Protector inside Meter Cupboard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
825
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
887
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock