Discuss Insulation resistance issue. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
This is a new 1 on me.
Testing a ring final circuit within a timber outbuilding.
All clear on insulation resistance with socket fronts connected but not screwed into metal back box lug. As soon as I connect any of the plates to the back box I'm getting around 16megohm between n and cpc. When all socket fronts connected getting around 2.2megohm. All I can conclude is that the neutral has been caught and is conducting through the timber frame (damp) to the backbox. What are your thoughts please.
 
Your analysis seems about right, that the neutral is leaking to part of the structure and hence to the back boxkes, but not to the earth terminal in the CU. As Snowhead says a normal 'divide and conquer' approach should find it.

There was a very similar thread (albeit involving the line conductor and breeze block walls) here: Previous low IR to back boxes thread
 
Have you split the ring to try to isolate the fault?
Snowhead,
The problem with that is I'm getting a reading irrespective of which socket is connected to backbox.
[automerge]1592602354[/automerge]
Your analysis seems about right, that the neutral is leaking to part of the structure and hence to the back boxkes, but not to the earth terminal in the CU. As Snowhead says a normal 'divide and conquer' approach should find it.

There was a very similar thread (albeit involving the line conductor and breeze block walls) here: Previous low IR to back boxes thread
Lucien, just read that previous thread you referenced , exactly the same issue. So what I need to do is disconnect all neutrals and individually test between each leg and screwed back front plate until I find the pairing ends. Got it
 
Last edited:
I had something similar on am existing installation, in this case a tw&e used as a pair of strappers for 2 way lighting, had just one of the cores nicked by a nail, into a plastered wall. If the back boxes do not have an earth fly lead, as suggested, screwing the back boxes back would make the fault connection.

In my case the actual fault was easy to find, it was nail fixing a dado rail directly below a landing switch. The dado rail had been installed some years prior.
 

Reply to Insulation resistance issue. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This is a 2/0 CU Feeder wire coming into the main subpanel on a 200A service. There are no nicks in the copper wire and from the front side...
Replies
3
Views
194
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock