Discuss Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

If you ask a question which betrays a significant lack of knowledge or understanding then you have to expect to take some flak.
If you were on site with an electrician, bearing in mind you are claiming to be in the same trade, you would receive a heck of a lot worse a reaction.

Calm down Dave, poor lads got to start somewhere. Dont forget your roots, i bet you weren't a perfect tester when you freshly qualified. Instead of the petty digs try helping him without sounding so condescending. Ive had some right nightmares testing when i was let loose from my am2, some school boy errors and some polish dry liners, either way i gained more experience and 1 am now a confident tester. Experience is key!!1
 
Just go back to basics, and perhaps another day and fresh head. Its your house, no rush just think about things and you will find the answer.
 
Thanks
No alarm connected.
Will do methodical as Dave suggested.
Forgive me for this but the only reason to test on 250v as far as I am aware is to protect sensitive equipment but I had every plug disconnected from the sockets and had nothing left connected. I know I don't need to unplug but just went round and unplugged everything anyway. Is there another reason I should test on 250v?

As has been mentioned earlier by others the most likely reason for this reading is that an appliance is still connected somewhere. A lot of people prefer to test at 250V initially just in case they have missed something.
 
So if there is still a load connected and I test at 250v would my reading be >200 Mohm meaning everything is good.

You see it's questions like this which just wind me right up, just stop and think about what you are asking for a minute!
What kind of load would have a resistance of >200 Mohm? A resistance of 200M would equate to a load with a running current of 1.2 micro amps, it's not going to be a very useful appliance!
 
Thanks for that. I have a fluke 1654b, not sure I it has a Kohm setting but will look into it.

That is a terrible meter to use for fault finding, an old school analogue insulation resistance and continuity tester is far more useful.
Personally I favour the robin K3131 but alternatives such as the megger BM7 are equally good.

Digital meters tend to focus your attention on the fine details of an exact figure to however many decimal places and can be easy to misread, an analogue meter gives you a far quicker and easier to identify yes/no.
Also with experience you can learn useful,information about. A fault by watching how the needle moves. Damp or water ingress will cause the meter to move differently to a fault of a fixed resistance or a loose/floating connection.


My favourite for this was a fault in a designer pendant with a 3m long chain. I found the fault when I accidentally knocked it with the ladder and my mate shouted that the needle on the meter had started moving back and forth, in fact it was moving exactly in time with the pendant swinging back and forth. The fault was the lamp holder being somewhat toasty
 
Thanks dave, I realise now what you are saying but I was thinking if a conductor was just very close to another but not actually touching somewhere would that not be similar to having bad insulation or am I still being simple.

I didn't have time to answer this properly earlier.
If you look up the dielectric strength of free air then you will see that the gap between conductors would have to be fixed at approximately 0.1mm for a dielectric breakdown to occur at the 500V test potential (this is some very rough approximation maths on my part, it will depend hugely on things like humidity and temperature and shape of the conductor)
If this breakdown does occur you will get an arc between the conductors, which is basically ionised air sitting between the two conductors across which energy will flow. I cannot say exactly how this would appear on a meter but I would expect it to either read as a dead short of it can sustain an arc or be an unstable value as the arc strikes and extinguishes randomly due to air currents cooling and distributing the ionised gas (the heat from the arc will create air currents)

But this is assuming you apply a constant 500V such as you would get from an analogue tester, but instead you are using a digital tester.
Now I am sure you have taken the time to actually find out and understand how your tester performs its tests and don't just push the button and read the numbers. So you will already know how the tester will vary the applied test potential based on the actual load and so the reading you get on the display I this situation should be obvious.
 
So if there is still a load connected and I test at 250v would my reading be >200 Mohm meaning everything is good.
well, obviously a reading >200Meg would indicate that there's no load resistance apparent.
 
well, obviously a reading >200Meg would indicate that there's no load resistance apparent.
Well that's what I thought so what would be the point of testing at 250v rather than 500v of its still gonna give me a reading as though a load is connected. Will be doing some more tests today anyway so will post results and hopefully find the problem.
 
Thanks
No alarm connected.
Will do methodical as Dave suggested.
Forgive me for this but the only reason to test on 250v as far as I am aware is to protect sensitive equipment but I had every plug disconnected from the sockets and had nothing left connected. I know I don't need to unplug but just went round and unplugged everything anyway. Is there another reason I should test on 250v?

Just be aware that some sockets only have sp isolation so you DO need to unplug everything to be sure.

Back to the op why are you doing this test? Is there a problem you haven't told us about? It's always best to post ALL information to avoid assumptions and guesses.
 
because a reading of > 200Meg. @ 250V tells you that there isn't a load connected. if it reads something like 0.1Meg. or less, then that says there's probably a load connected and by using 250V, you won't have fried it.
 
Just be aware that some sockets only have sp isolation so you DO need to unplug everything to be sure.

Back to the op why are you doing this test? Is there a problem you haven't told us about? It's always best to post ALL information to avoid assumptions and guesses.
No problems just practicing with my tester and those were the readings I got so it's good for practice to find out why and do some problem solving in my own house.
 
No problems just practicing with my tester and those were the readings I got so it's good for practice to find out why and do some problem solving in my own house.

Ok. So methodical testing will find the issue or appliance. All you need is time, patience, a pencil and some paper.
 
Ok. So methodical testing will find the issue or appliance. All you need is time, patience, a pencil and some paper, a supply of smokes and beer, and loads of patience.

modded that for you murdoch. :toilet:
 
Well that's what I thought so what would be the point of testing at 250v rather than 500v of its still gonna give me a reading as though a load is connected. Will be doing some more tests today anyway so will post results and hopefully find the problem.

A lot of people prefer to do the 250V test as it is less likely to write off delicate equipment. I'm not entirely convinced that sensitive equipment is going to survive a 250V DC test any better than a 500V DC test, but then the kind of sensitive equipment I am used to encountering is along the lines of vintage studio mixing desks worth tens of thousands of pounds. I always specify that it is the customers responsibility to switch off and isolate, or at least supervise me isolating, the equipment.

Personally I prefer a standard resistance measurement first to identify any connected loads of i am in doubt.
 
Had a busy day today but managed to do a test on the circuit.
r1= 0.60ohms
rn= 0.61ohms
r2= 1.04ohms

Calculated R1+Rn= 0.3025ohms
Actual R1+Rn= 0.34ohms

Calculated R1+R2=0.41ohms
Actual R1+R2=0.45ohms

Insulation resistance test
Single circuit @ 250v
L-N = 0.01Mohms
L-E = >200Mohms
N-E = >200Mohms

Split the circuit and did as you said and found that it's the last run of cable between the last socket and CU but looking up the side of the boiler there is a single run of T&E leading to another fused spur but not had time to investigate it yet. At least I know where it is now.
Thanks will post what I find.
 

Reply to Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
586
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
739
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock