Discuss Insulation resistance testing Lighting circuit in the Commercial Electrical Advice area at ElectriciansForums.net

J

Joseph Lewis

Hi everyone. I'm looking for advise on how to test IR on commercial lighting. There's so many lights on 1 circuit , do I have to take out all the lamps in all the lights to perform the test or can I simply test between LN -E ?
Even though I have spent lots of time testing domestic installs and lots of installation work in commercial I lack experience testing it. And advice would be great
 
Disconnect neutral and just do L/E and N/E this is perfectly acceptable for an EICR. If you get any zero Meg readings it could be crossed neutrals. So if you get two or three zero readings disconnect all neutrals and retest, if you get okay readings it is crossed neutrals.
 
Thanks for you reply.
So I just disconnect neutral from each light fitting ? Or at the board ? And its OK to do the test at 500v?
 
Last edited by a moderator:
Thanks for you reply.
So I just disconnect neutral from each light fitting ? Or at the board ? And its OK to do the test at 500v?
At the board, do it at 500V. Lighting rarely incorporates filters which trigger at 500V to give false readings. If the reading is down at 500 it will be down at 250. You could get all sorts of readings but anything above 2 Meg should be considered satisfactory. Don't forget my previous Post about crossed neutrals it is very common.
 
I should also say as a safety issue, if you cannot isolate the board, because it isn't always practical be careful disconnecting the neutrals in case they are not to terminal order. Pull one out and it is the wrong one can lead to arcing and if you are not overly experienced in testing can cause hazardous reactions, take care.
 
96060"]Disconnect neutral and just do L/E and N/E this is perfectly acceptable for an EICR. If you get any zero Meg readings it could be crossed neutrals. So if you get two or three zero readings disconnect all neutrals and retest, if you get okay readings it is crossed neutrals.[/QUOTE]
I should also say as a safety issue, if you cannot isolate the board, because it isn't always practical be careful disconnecting the neutrals in case they are not to terminal order. Pull one out and it is the wrong one can lead to arcing and if you are not overly experienced in testing can cause hazardous reactions, take care.
Thanks for the advise , a great help . I will be very careful disconnecting the neutral
 
Hi everyone. I'm looking for advise on how to test IR on commercial lighting. There's so many lights on 1 circuit , do I have to take out all the lamps in all the lights to perform the test or can I simply test between LN -E ?
Even though I have spent lots of time testing domestic installs and lots of installation work in commercial I lack experience testing it. And advice would be great
Keep going at it the more you do the better it becomes to overcome these problems and you get to understand the unexpected reading you may get
 

Reply to Insulation resistance testing Lighting circuit in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
583
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
816
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
754
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock