So i have db1 in 1 block of flats for communial lights etc, feeding db2 via a swa feed underground. Ir at db1 to test every circuit and submains 0.01Mohms. (N+L together to earth)
Switch db2 off. All clear. Db2 also all clear when testing ir when investigating further.
Any suggestions??
 
Isolate every circuit completely at both boards and make sure all equipment is unplugged or fully isolated and test each section in turn , simple ....
 
From what you describe, everything correctly wired and DB1 and DB2 with DB2 on are 0.01MΩ and with DB2 off is >200MΩ and all of DB2 is >200MΩ there can only be fault within the main switch of DB 2 to earth!

Since this is not possible unless there is a huge metal spike through the switch there is something missing. Did you test DB1 and DB2 together after testing DB2 as clear as it may have then been OK.
Perhaps someone realised you were testing and removed the offending item.
(I have had this; testing a circuit found the fault left one faulty cable, one OK cable sticking out went to get a new cable, test again and both cables are now at fault, the customer had been "helping" by plugging everything back in, as I was nearly finished!)
 
From what you describe, everything correctly wired and DB1 and DB2 with DB2 on are 0.01MΩ and with DB2 off is >200MΩ and all of DB2 is >200MΩ there can only be fault within the main switch of DB 2 to earth!

Since this is not possible unless there is a huge metal spike through the switch there is something missing. Did you test DB1 and DB2 together after testing DB2 as clear as it may have then been OK.
Perhaps someone realised you were testing and removed the offending item.
(I have had this; testing a circuit found the fault left one faulty cable, one OK cable sticking out went to get a new cable, test again and both cables are now at fault, the customer had been "helping" by plugging everything back in, as I was nearly finished!)

Im certain nobody touched anything being as it was the communial installation. Very strange though. But a ir test at db2 to prove no faults didnt really require another test back ad db1 being as all was clear.
 

Reply to Insulation Resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
740
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock