Discuss Insulation test on shower with neon switch in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
Doing an insulation resistance test on a shower, can someone explain how to bypass the neon in the isolator? Do most people chock block bypassing neon or another way?
Also for a lighting circuit with flurocents?
Thanks
 
When doing an insulation resistance test on most circuits with a load across live and neutral, you need to put one probe of your tester to live and neutral at the same time and the other probe to earth. No chock blocks needed at switches or isolators. :) I just remembered, in a lighting circuit with a dimmer switch you need to bypass the dimmer switch.
 
Last edited:
Shouldn't need to, are you doing an EICR. Just carry out the test to earth only omitting the line/neutral test.
 
Doing an insulation resistance test on a shower, can someone explain how to bypass the neon in the isolator? Do most people chock block bypassing neon or another way?
Also for a lighting circuit with flurocents?
Thanks
L and N linked test to earth
 
When doing an insulation resistance test on most circuits with a load across live and neutral, you need to put one probe of your tester to live and neutral at the same time and the other probe to earth. No chock blocks needed at switches or isolators. :) I just remembered, in a lighting circuit with a dimmer switch you need to bypass the dimmer switch.
OT big time I'm afraid so apologies. Had8Lives - is your pic a silver studded blue?

View attachment 35544
 
That's why the Crabtree pull switches are so good, drop the cover down and the neon is disconnected. Pointless though if the shower has always on neons etc.
 
Indeed. But that doesn't alter the fact that AGREED limitations must be agreed!
Mmmm, I'm not quite sure I am following this. If I said to a customer "right I am only going to do the IR test with the line and neutral conductors linked and just tested to earth, rather than......." I think they might give me a bit of an odd look. Mind you it is Derbyshire......
 
Mmmm, I'm not quite sure I am following this. If I said to a customer "right I am only going to do the IR test with the line and neutral conductors linked and just tested to earth, rather than......." I think they might give me a bit of an odd look. Mind you it is Derbyshire......
I don't disagree, but unfortunately we don't actually have any choice in the matter!
 

Reply to Insulation test on shower with neon switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
600
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
I'd like to wire a six pin DPDT rocker toggle switch to turn a low voltage LED fixture on and off. The rocker toggle switch I have is an...
Replies
1
Views
753
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock