Discuss Interconnection of MV Earth with LV Earth in Public Supply in the UK Electrical Forum area at ElectriciansForums.net

Cookie

-
Reaction score
117
What factors determine the interconnection of the MV neutral/earth with the LV neutral at the local substation? When are they connected together and when would it be appropriate not to connect them together?
 
The rule of thumb is when the combined value is below one ohm they can be connected.
HV has to be below 40 ohms, LV has to be below 20 ohms, 8 meters separation between them.
Measurements taken before any cables are connected.
 
What factors determine the interconnection of the MV neutral/earth with the LV neutral at the local substation? When are they connected together and when would it be appropriate not to connect them together?
HV,LV whats MV? thought MV was old hat.
 
Nope

ELV, LV, MV, HV, EHV etc all still very well defined.

it is only the wiring regs that simplifies everything above LV as "HV"
wheres does MV Start and HV kick in? and where does it state the parameters ?
 
wheres does MV Start and HV kick in? and where does it state the parameters ?
Iec 60071 defines MV as 1kV to 36kV

Most others take the value as 35kV (such as iec60038)

HV is 35kV to 230kV
EHV >230kV

So the usual distribution in the UK is MV (6.6/11/22kV)

Primaries are usually 33kV but could be 66kV, some grid is 66 or 132kV - all HV.

but the bulk transmission is 232kV and 400kV (EHV), although some was 132kV (HV) up to a few years ago - not sure now.

Some transmission towers carried both 132 and 232 in the North West, and some carried 232 and 400kV - for example galloping gertie between Darwin and Bradford.


Edit : apparently gerty is spelt gertie - but neither looks right to me!
 
Last edited:
Interesting- thanks!

Does the grounding at the HV-MV substation play any role? I've heard that MV systems in the UK are resistance or peterson coil earthed. Is this true?
 
Most power distibution is at 132kv (highest voltage for a DNO), 275kv and 400kv. I've never seen or heard of 232kv.
 
Does any one know why the voltage thresholds were chosen?

I'm assuming they are phase-neutral (i.e. earth) since the main risk of shock is touching a line conductor while in contact with the Earth (or attached parts), and I am guessing that the 1kV LV/MV(HV) threshold is related to dry skin breakdown / arc risk where the shock current is much more then 1000/230 sort of scale factor.

But is there some aspect to HV engineering that makes ~35kV a point where different techniques, etc, have to be used to justify the MV/HV category?
 
Last edited:
I'm assuming they are phase-neutral (i.e. earth) since the main risk of shock is touching a line conductor while in contact with the Earth (or attached parts)
At EHV you don't have to worry about touching a live conductor. You would be dead well before you touched anything. NG safety distances are 1.4m at 132kv, 2.4m at 275 and 3.1m at 400kv but in reality it's 'as far away as f'in possible'.
 
Most power distibution is at 132kv (highest voltage for a DNO), 275kv and 400kv. I've never seen or heard of 232kv.
A reasonably quick way to tell the voltage of a pylon. If it's just got 1 cable per phase it's 132kv. 2 cables is 275kv and 3 or 4 is 400kv.
 
Interesting stuff,

I thought HV power distribution was delta, so no neutral (star point)

I have no basis for this, other than my own conclusion from looking at 3 wire overhead lines, going to what i presumed were delta to star transformers to step voltage down to 230v (415v) and provide a neutral / earth for consumers??
 
I wouldn't do that job for any money! I wouldn't climb the pylons either. I'm happy when I'm just climbing about all over the transformers ?
 
Interesting stuff,

I thought HV power distribution was delta, so no neutral (star point)

I have no basis for this, other than my own conclusion from looking at 3 wire overhead lines, going to what i presumed were delta to star transformers to step voltage down to 230v (415v) and provide a neutral / earth for consumers??

Transmission and distribution is 3 wire, however the network is still earthed, the star earthing point is generated either by the "upstream" transformer or more commonly a seperate earthing transformer - it has a special winding called zigzag, and no secondary.

The connection to earth is often through a resistance, or reactance to limit current, it also reduces the possibility of circulating current through the earth if the network ends up earthed at multiple locations (generally avoided).
 
I wouldn't do that job for any money! I wouldn't climb the pylons either. I'm happy when I'm just climbing about all over the transformers ?
Nope, the same, I have had little to do with transmission stuff in a practical sense.

Too high, too many volts, too scary...

Only been involved in the protection side of it, so far far away...


Edit:

I remember one of my university friends was at CEGB and did a lot of work up transmission towers - didn't seem bothered about it at all, perhaps it was bravado as when he told us we were all absolutely terrified just hearing about the work!
 
Last edited:
Does the grounding at the HV-MV substation play any role? I've heard that MV systems in the UK are resistance or peterson coil earthed. Is this true?
LV networks are always solidly earthed and may be TT TNS or TNC-S.
The main distribution voltage is 11kV although other voltages are used. The 11kV network can be solidly earthed or resistance earthed through liquid or dry resistors. Peterson or arc suppression coils are used occasionally in some areas where the network is mainly overhead.
33kV and 132kV can be either resistance earthed or use an earthing transformer. 275kV and 400kV usually have earthing transformers.
There is no neutral conductor in HV but the starpoint of a star winding is usually earthed either solidly or through a resistance as above.
Earthing transformers have a zigzag primary which creates a starpoint for earthing through a resistor. The secondary of the earthing transformer is 400/230V and is used to supply power for the substation ancillary's.
This is a very general view of earthing arrangements, various voltages and earthing arrangements are used throughout the UK.
 

Reply to Interconnection of MV Earth with LV Earth in Public Supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
938
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
699
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
452
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock