Discuss Interesting video on testing type "A"'s RCBO and issues with MFT 's in the UK Electrical Forum area at ElectriciansForums.net

Watched it yesterday.
The main thing they were plugging was that BS7671 tables for testing RCDs only apply to type AC RCDs. Therefore, the ECA chap was recommending that we test all RCDs on the type AC setting on our test equipment, regardless of the type of RCD under test.

Then the Lewden technical chap added that, for a type A, we should test first on the AC setting, then test again on the A setting. The results we record would be the results from the type AC, as this is what BS7671 is asking for on the schedule of year results.

Interesting discussion indeed.

They also touched on where in the circuit we should be testing RCDs....
 
I've watched this twice now and it is a bit of a WTF moment.

It looks like everyone is looking at each other to figure out how the hell we ended up in this mess.

Manufacturer is getting massive returns as the devices are "failing" their answer is they're not failing by the specs that we use but don't publish.

MFT maker just looking blank.

The ECA chap made most sense with his "just test AC type as its the only test we have published targets to test against"

More comedy from the electrical industry.
 
I've watched this twice now and it is a bit of a WTF moment.

It looks like everyone is looking at each other to figure out how the hell we ended up in this mess.

Manufacturer is getting massive returns as the devices are "failing" their answer is they're not failing by the specs that we use but don't publish.

MFT maker just looking blank.

The ECA chap made most sense with his "just test AC type as its the only test we have published targets to test against"

More comedy from the electrical industry.
Well I'm not surprised to hear this

I reckon there's definitely a knowledge gap to be filled in regard to testing of A and B type

Thankfully we don't series the RCDs over here which complicates matters a little further


Now maybe everyone is fully up to speed but I could see where I was mistaken a few minutes into the video
 
What gets me is that megger are basically selling a lie and their tester can't properly test the type A B or F properly as it doesn't meet the manufacturer standard for testing them but does meet their standard for testing them wtf!
And that the manufacturer doesn't want to give up their standard information as they have probably paid a fortune to acquire it so they can make things to those standards.
That has really made my brain hurt!
 
What gets me is that megger are basically selling a lie and their tester can't properly test the type A B or F properly as it doesn't meet the manufacturer standard for testing them but does meet their standard for testing them wtf!
Megger are supposed to be top brand, me if I worked there I would start throwing the testers out the window and starting again.
 
What gets me is that megger are basically selling a lie and their tester can't properly test the type A B or F properly as it doesn't meet the manufacturer standard for testing them but does meet their standard for testing them wtf!
And that the manufacturer doesn't want to give up their standard information as they have probably paid a fortune to acquire it so they can make things to those standards.
That has really made my brain hurt!
I think the tester works it's just that there is nothing to relate the results to as that I the manufacturer's proprietary information and, for all we know they may well al be different.
 

Reply to Interesting video on testing type "A"'s RCBO and issues with MFT 's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
294
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
983
Hello everyone, Is it necessary to test RCBO x5? Some say that you can’t even test at x5 times because it can damage RCBO. Others that you can...
Replies
4
Views
965
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
671
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock