Hi I was wondering if someone would be able to tell me or explaine how many combinations an intermidiate switch has when it come to r1+r2 testing, I know a 2 way lighting circuit is 6 but I can't remember about intermidiate circuits.
any help would be appreciated thanks
 
3 wire crossover.jpg
Seems like 8.
However the intermediate switch position will (should) not change the reading for R1+R2 if you have done all the options for the end switches.
Also note that when the light would be on all the line conductors are covered for insulation testing
 
I know a 2 way lighting circuit is 6

Not sure what you mean here, there are only 4 combinations of switch positions, 2²=4. For three two position switches 2³=8 but as Richard says the intermediates don't disconnect anything so don't remove any conductors from the test regardless of their positions.

Also note that when the light would be on all the line conductors are covered for insulation testing

I think this needs qualification. If the switches are wired with the PL and SL paralleled to the L1 & L2 strappers, then when the light is on all conductors are live and get tested in a single test. OTOH if the PL and SL go to the commons of the two switches (as you might do when wiring in singles) then when the light is on, one strapper is floating and does not get tested until both 2-ways are flipped over to the other on position.
 

Reply to Intermidiate switching combinations in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
547
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
626
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
863
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
The house I've just moved into is fitted with the light switches shown in the pics. They are fitted to each bedroom and the landing. The landing...
Replies
9
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock