We plan to upgrade our 500w inverter to a 3000w inverter in order to accommodate a .75hp water pump (used only three times per week for 20mins), a small fridge and a couple of standing fans. We currently have 4 x 120w solar panels, 2 x 24v batteries and a Vitron Blue Solar MPPT 100/50 charge controller. Can you please advise whether any of these pieces of equipment need to be changed in order to work with the larger inverter. Many thanks
 
That will be a big increase in battery draw, about six times, from say 20A to 125A.
What is the type and rating of your batteries - are they lead acid or Lithium or ??, and how many AmpHours etc?
While you may only need 20 minutes of high current via the 3 kW inverter for the pump, if that depletes the lead acid batteries more than say 30%, it could shorten their life considerably.
 
Lead acid 100Ah
That will be a big increase in battery draw, about six times, from say 20A to 125A.
What is the type and rating of your batteries - are they lead acid or Lithium or ??, and how many AmpHours etc?
While you may only need 20 minutes of high current via the 3 kW inverter for the pump, if that depletes the lead acid batteries more than say 30%, it could shorten their life considerably.
 
Thanks. So you have two 100Ah 24V batteries in parallel?
Assuming the batteries are fully charged before you run the pump for 20mins (on the new 3kW inverter) with nothing else using power, I think you should just be OK. Need the right gauge of wiring obviously!
I have no experience of solar systems, so I hope someone else with more knowledge comes along to help ?
 

Reply to Inverter upgrade in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
845
Hi All We're new here and looking for some advice to make sense of the world of leisure batteries and inverters. We're setting up a coffee van...
Replies
7
Views
5K
hello guys this is my first post, i hope I am posting this one on the right section. aamseee I am looking for some advise. i have bought a...
Replies
1
Views
3K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
M
Hi Folks, I am looking for some way to optimize my home PV system of 4 panels 235Watts each sitting in sequence and connected throug MPPT charge...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock