EICR under taken again on property.
Insulation Resistance results on at 500V. All results in Mega Ohms
LIGHTING L-N 34.80, L-E 2.05, N-E 33
LIGHTING L-N 2.47, L-E 2.97, N-E 2.81
UP POWER L-N 78, L-E 72, E-L 69
DOWN SOCKETS L-N 16.30, L-E 15.41 N-E 44.43

Everything unplugged and all lamps taken out
I am concerned about both lighting circuits and down sockets.
What would cause such readings? And what do i put down on cert? Code 3? or Note?

Any help/advice would be much appreciated :)
 
put your readings in the appropriate columns. as all are > 2 megohms, then there;s no need for anycodes or comments.
 
As mentioned,no issues as per regs,but i would be intrigued to discover the reason...much more information needed,that lighting circuit is very even...may be groovy,if it supplies perimeter illumination for a 4 acre garden ;)
 

Reply to IR Problems/Questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
I had just installed a heat alarm on the downstairs lighting circuit during a kitchen rewire. The new kitchen ring / cooker circuit I tested IR...
Replies
4
Views
3K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock