Discuss IR testing results on MWC in the UK Electrical Forum area at ElectriciansForums.net

N

NickD

Interested to know what other people do about IR testing results on a MWC. If your additions contain new fixed wiring then you test that and record those results, obviously. But what if you're just replacing a fitting with a brand new one, the IR testing of which seems pointless? Do you leave blank or strike through these entries (which are in a section called "Essential Tests")? You're not under any obligation to IR test the existing wiring you're connecting/adding to to sign off the MWC IMHO.
 
Strictly speaking you should be carrying out the proper tests in accordance with BS7671, sub missing put the IR test IMHO is not a good idea, you could just do a limitation test, reg 614.3.2 if I remember correctly.
 
Strictly speaking you should be carrying out the proper tests in accordance with BS7671, sub missing put the IR test IMHO is not a good idea

So what would you IR test if just swapping out a fitting? The (new, boxfresh, certified fit for purpose by manufacturer) fitting? The existing wiring, maybe having to open up the CU when you otherwise didn't need to?
 
So what would you IR test if just swapping out a fitting? The (new, boxfresh, certified fit for purpose by manufacturer) fitting? The existing wiring, maybe having to open up the CU when you otherwise didn't need to?

Why are you carrying out a full sequence of tests on a like for like replacement?!

Check it's earthed if applicable and that it will meet disconnection times, replace, pack up, jog on to the next job. You're just wasting time and lumbering yourself with unnecessary paperwork!

- - - Updated - - -

Ze ??? :detective:

Beat you to it! lol
 
Why are you carrying out a full sequence of tests on a like for like replacement?!

Check it's earthed if applicable and that it will meet disconnection times, replace, pack up, jog on to the next job. You're just wasting time and lumbering yourself with unnecessary paperwork!

- - - Updated - - -



Beat you to it! lol

Only just....but it's still on my post.lol!
 
Why are you carrying out a full sequence of tests on a like for like replacement?!

I'm not, that's my point, I wouldn't IR test and I strike through the IR test results (while trying to ignore the heading above that says "Essential Tests", implying none are optional). I Zs, I generally do a final earth continuity test once it's fitted (just to preclude CPC having popped out of block or whatever) [=extra 2mins], I RCD test [=extra 2mins]if it's RCD protected and the customer doesn't mind the affected circuits going down.
 
Why are you carrying out a full sequence of tests on a like for like replacement?!

Check it's earthed if applicable and that it will meet disconnection times, replace, pack up, jog on to the next job. You're just wasting time and lumbering yourself with unnecessary paperwork!

- - - Updated - - -



Beat you to it! lol

That makes sense Mr DS.. What would you do if there was a little more to the job? For example if you've added a light to existing circuit.. just a simple one, say an extra light up in the loft. Would you then do all the required IR tests for the MWC? The job has taken perhaps 15 minutes, but you now have to take out all light bulbs in the whole house (all on one circuit) and hope that nothing else is on the lighting circuit that you have to hunt down..

My point being is do you ALWAYS do a L-N IR test when doing small jobs (not like for like) and if not what would you put on the MWC?

- - - Updated - - -

On a minor works cert then, what do you put in the IR reading box if you don't do it?

Good point..
 
I'm not, that's my point, I wouldn't IR test and I strike through the IR test results (while trying to ignore the heading above that says "Essential Tests", implying none are optional). I Zs, I generally do a final earth continuity test once it's fitted (just to preclude CPC having popped out of block or whatever) [=extra 2mins], I RCD test [=extra 2mins]if it's RCD protected and the customer doesn't mind the affected circuits going down.
you verefy by visual and appropriate test/s that the circuit you are replacing an accessory on is good for continued service...

and that its good for any extra load/s that may be placed on it...

in the case of replacing an accessory this could take the form of a quick Zs....
 
Opotion 4 = don't bother filling in a sheet at all lol

Option 5 is i left my testers on another job, being calibrated , or any other excuse i have seen on here that they didnt test.
Or option 6 is that a flapping leaf blowing on the terminals prevented any testing. I miss JRC:rofl:
 
What would you do if there was a little more to the job? For example if you've added a light to existing circuit.. just a simple one, say an extra light up in the loft. Would you then do all the required IR tests for the MWC?

I then do and record the required IR test for the MWC, which is the addition in the loft, with the CPC connected but before connected L&N, testing only the new wiring, ignoring the existing wiring.
 

Reply to IR testing results on MWC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
634
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
902
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I had just installed a heat alarm on the downstairs lighting circuit during a kitchen rewire. The new kitchen ring / cooker circuit I tested IR...
Replies
4
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock