Carried out an EICR on an older installation at the start of the week prior to a mains board swap over. I had a low reading on one of the ring main IR tests, between live & neutral 0.02MOhms. I couldn’t see anything plugged in or switched on anywhere on the circuit & at that point I couldn’t gain access to the attic to see if there was anything that could affecting the test as the customer was away & it was locked. The live to earth was 150m Ohms, neutral to earth 185m Ohms. I swapped the mains over today & the circuit isn’t tripping the RCBO. If it was a fault in cable would that reading cause it to trip? Customer is home start of next week so can’t gain access to attic until then.
 
Just IR test to earth with the line and neutral connected together. Forget line to neutral readings on periodics unless you can be certain there is nothing connected across them. Why would the rcbo trip?
 
Last edited:
You could measure the continuity between L and N to help identify whether a load is connected or not.
You could also measure the current flowing through the circuit to establish whether something is connected.

Neither of these is infallible, but it will help you to understand what is going on.

An IR of 0.2Mohm between L and N is unlikely if the IR to earth is 150Mohm (I assume the m in the OP was supposed to be M)
 
The live to earth was 150m Ohms, neutral to earth 185m Ohms. I swapped the mains over today & the circuit isn’t tripping the RCBO. If it was a fault in cable would that reading cause it to trip?

It always puzzles me when an electrician asks this sort of question. We all learned ohms law at school, and use it regularly, and we all understand what causes an MCB, RCD, RCBO etc to trip so should be able to answer this.
The resistance between L and N is 0.02Mohms, which is 20,000 ohms, so you can calculate the current flow resulting from this using V=IR.
240/20,000=0.012A
So there will be 0.012A flowing between L and N.
Since that is significantly less than 32A no it won't cause the OCPD to trip.

Even if that was the IR to earth it wouldn't be enough to cause a 30mA RCD to trip.
 

Reply to IR value on ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
886
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock