Got a customer who's wanting a washing machine and tumble dryer in the bathroom.

Normally the solution is to hard wire into FSUs but he's come up with the solution of kitchen units and a work top with the sockets in the void between the wall and the back of the units.

Could this be argued to be outside the zones?
 
Got a customer who's wanting a washing machine and tumble dryer in the bathroom.

Normally the solution is to hard wire into FSUs but he's come up with the solution of kitchen units and a work top with the sockets in the void between the wall and the back of the units.

Could this be argued to be outside the zones?
What's your opinion?
 
Got a customer who's wanting a washing machine and tumble dryer in the bathroom.

Normally the solution is to hard wire into FSUs but he's come up with the solution of kitchen units and a work top with the sockets in the void between the wall and the back of the units.

Could this be argued to be outside the zones?

you tell me your opinion and I will share mine!!

oh ok, I would consider it outside of zone.
 
Wondering really (hence the post). On the face of it , the spirit of the reg is there to stop e.g someone using a hairdryer in the shower. Unlikely to happen if they have to pull the washing machine out first. However the socket isn't actually in a cupboard with a closing door.

there is always a difference opinion between following the reg's like a blindman follows his dog,
and the people who understand the reg's and follow them to the letter where it is important. but follow them in both principal and intention (spirit of the reg) in practice, without ever reducing safety but applying a can do approach. it is not an easy choice sometimes but your moral standings should guide you to one side of the fence or the other.
 
you are right, the book provides the answers.

however, just to counter the argument, what stops someone hosing down the contents of there kitchen with the garden hose that is just outside the kitchen door?

we all work in an environment that is all about reducing risk, however there are some risks that you have to consider to be irrelevant because only sheer stupidity would put you in danger?

do we put barriers up along every road incase someone is stupid enough to walk blindly into it?
do we put safety switches on car bonnets that stop the engine when we lift them incase someone sticks there hand in moving parts?

it is all about risk assesment. unfortunately the regs give little space for that so we have to apply them with the best of our knowledge and experiance.

p.s. i am a little bit ----ed now so don't take my word as gospel!!!
 
It’s a bit ambiguous anyway as I’ve seen much like everyone else on here 100’s of bathrooms with a socket just out side the door.....sometimes less than 1 meter let alone 3....but it’s outside the room so....I think I’d want to see cupboard doors in the units personally
 
however, just to counter the argument, what stops someone hosing down the contents of there kitchen with the garden hose that is just outside the kitchen door?

Nothing stops them from doing that, but accidentally dropping the shower head or the shower head falling out of its holder and spraying the room is a more likely accident.

I know I've accidentally sprayed most of the bathroom when washing the dog, and when washing dye out of my hair.
 
The regs are very black and white when it comes to bathrooms... or "rooms containing a bath or shower" so if there was an incident after you had fitted a socket in a bathroom even behind an appliance.... your insurance co, or your scheme will not back you up.

Grey area would be a WC. Where ive seen new builds with the consumer unit above the basin. Still loads of water to splash about.

In my own house, I can stand in the shower cubicle, with the shower screen open and the door open, I can touch the lightswitch. Perfectly acceptable regs wise, as its outside the room... but unlikely to happen. not impossible.
 
Yeah, what colour?
and do you diet?
Sorry , it's a bit late, so no offence meant!

On the topic, I think its not compliant, but in Spain it is very common to find a washing machine in the bathroom, pluffeg in to a socket in an area we would define as not allowed...they don't drop dead...
However, the regs there are tightening up, so if you have an electrician in to do work, they will remove the sockets which are beside the whb, fit a blanking plate, and leave the innards for you to refit later.
[automerge]1583446266[/automerge]
With you on that littlespark...new-builds with CU in downstairs WC...I just don't like it, especially where you have to stand on the loo to inspect the CU. Just daft, frankly...but then you all know my views on new builds...
 
What colour do you dye it ??

Various colours, usually blues and purples but occasionally reds.

IMG-20181223-WA0000.jpg


IMG_20190501_064217.jpg
 
Never seen one, @Baddegg , except the picture on this forum somewhere when the boiler was mounted to the wall directly above the bath!
Possibly in the section titled “WTF!”
See em all the time down here @littlespark, the houses are mostly old Victorian and weren’t built with indoor bathrooms so are small additions, quite common to have the boiler in the bathrooms albeit in a cupboard with a door on and fed through a fused spur....
 
I tell a lie. Seen them in some static caravans, behind a cabinet door, other side of the room to the shower. But still got to clamber over a toilet pan to reach it
 
I don't know the current (pun alert) zone restrictions in the UK, but in France they are zone 1 immediately above the bath/shower and 2.25m above the bottom of either, zone 2 is 600mm beyond the edge of those anything beyond that is not classed as a zone, sockets, switches and appliances can be in that area, there are some other extensions to the zones for projecting shower heads where the volumes of both zones are extended, but then all circuits in France are protected by RCD's in my own place the bathroom/shower rooms are all protected by individual RCBO's to each appliance, radial and lighting, thought it may be of interest and promote some discussion on the safety of RCD/RCBO's within a potentially wet area.
 

Reply to Is a socket in a cabinet outside the zones in a bathroom? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Replies
23
Views
3K
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
653
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
928
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
771
Rewiring an old farm cottage… every wall brick and previous wiring not done well at all. I can’t locate any of the prescribed zones diagrams on...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock