Discuss Isolation Fault in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
2
On submitting FIT meter readings to the electric supplier, notification was received that there was a discrepancy between the most recent readings and those previously submitted. On checking, it was found that there was a big discrepancy between the FIT meter fitted by the solar contractor (now gone bust) when compared to the readout obtained at the Samil invertor. A contractor was brought in, who confirmed the meter was faulty. They supplied and fitted a replacement meter. On completion; everything was accepted as being in working order i.e. readings taken at the new meter and compared with the invertor showed that reading where in sync.
However, days later the invertor was found to be displaying an error message "Isolation Fault". Pressing the invertor reset button still produced the same error message. Attempts to get the contractor to return have not been successful. Now a strange thing occurred. Pressing the reset button (something done on numerous occasions without success)the error message cleared and generation took place and continued all day. Unfortunately the following morning generation had stopped, the error message reappeared until the reset button is pressed. This procedure has to be repeated daily.
Any suggestion as to the cause of this problem and how it can be cured.
 
Hi, welcome to the forums?

Do you have any form of we based management facility? If so, it may help the guys who deal with solar regularly if you could grab the inverter logs and upload them here so they can have a read.
 
"Isolation Fault" on a PV inverter means you have a break down between the DC side and earth. The inverter checks for this on start up. It may be condensation and borderline which is why if you can get it to start it will run for the rest of the day. Of course it then shuts down overnight and has to restart in the morning.
Dont just get any spark round, get someone who works with and understands PV to isolate the DC from inverter and get their megger out of its box.
 
"Isolation Fault" on a PV inverter means you have a break down between the DC side and earth. The inverter checks for this on start up. It may be condensation and borderline which is why if you can get it to start it will run for the rest of the day. Of course it then shuts down overnight and has to restart in the morning.
Dont just get any spark round, get someone who works with and understands PV to isolate the DC from inverter and get their megger out of its box.
 
Thank you. The isolation error message only appeared after a replacement FIT meter was fitted. The old meter was about the size of a MCB, very very difficult to read because of it's size, it was located in a control box into which the AC from the invertors was fed. Along side the "small" meter were 4 trips in pairs. The AC feeds (from invertor) colour coded brown and blue connect into the top the first pair of trips. From the tops of the other pair of trips there are two cables, these connect via an isolator, to the domestic db. What puzzles me is there is a single blue wire from the bottom of the first pair of trips to the corresponding "blue" side of the second pair. In other words there is no corresponding link of "brown" to "brown" (feed from inverter). The question is should the the trips be linked in the conventional way .I.e. Blue to Blue and Brown to Brown. If the link had been omitted when the old meter was removed, could this lead to the error message.
 
The "isolation fault" you mention will be on the DC side not AC.

What kW system size are we talking about here and how many inverters do you have on it?

As above, some photos would be pretty helpful if you can.
 
There should be a link above the reply box, if you do not have it,you may have to reach a certain number of posts.
Perhaps a Mod can confirm.
Hello again. In the process of taking some photographs, (still can't find out how to post them when I get them) we removed the covers so that the wiring and interiors of the switch units could be clearly seen. The link that I thought originally was missing was there. On checking further; T&E cable had been used to connect the AC out put to the new FIT meter. However, the removal of covers showed that although the new meter was earthed, there was no earth continuity connection to the rest of the equipment. An earth conductor was wired in and the error (Isolation) message has disappeared. Observations over the last few days indicates that the inverter appears to be performing correctly and no error message. At this time I hope that will be that but!!! One difficulty is that I don't have sufficient experience to do further trouble shooting and can't find a repairer with the knowledge to fault find and repair. Someone located in the Cheshire/ Warrington area, if further trouble occurs.
All observation welcome.
 
I would still check out the DC side as "Isolation Fault" with regard to PV specifically a DC to Earth Issue.

Out if interest, Is your array bonded to MET?

In any case, during daylight with panels producing, meter set to VDC test between DC + to Earth (cpc prob most convenient) and DC - to Earth. See if you have any voltage and report back :)
 
I would still check out the DC side as "Isolation Fault" with regard to PV specifically a DC to Earth Issue.

Out if interest, Is your array bonded to MET?

In any case, during daylight with panels producing, meter set to VDC test between DC + to Earth (cpc prob most convenient) and DC - to Earth. See if you have any voltage and report back :)
Hi. Some back ground. The system was installed by Solar King in 2013. It has a Samil inverter and 12 PV roof panels.
Because of my lack of mobility, all my activities have to be at ground level and I can't check if the panels are bonded by a separate earth cable. However, the metal work of the control panel that houses the trips ( input from FIT meter and output to the DB) is connected to MET.
When I check for DC voltage to earth, what level of reading should I expect to find for a good or fault condition?
Thanks again.
 
to upload photos to the forum, click the "upload a file" button (bottom right of reply window) and then select the file to upload.
 
Hi. Some back ground. The system was installed by Solar King in 2013. It has a Samil inverter and 12 PV roof panels.
Because of my lack of mobility, all my activities have to be at ground level and I can't check if the panels are bonded by a separate earth cable. However, the metal work of the control panel that houses the trips ( input from FIT meter and output to the DB) is connected to MET.
When I check for DC voltage to earth, what level of reading should I expect to find for a good or fault condition?
Thanks again.
 
Hi. Some back ground. The system was installed by Solar King in 2013. It has a Samil inverter and 12 PV roof panels.
Because of my lack of mobility, all my activities have to be at ground level and I can't check if the panels are bonded by a separate earth cable. However, the metal work of the control panel that houses the trips ( input from FIT meter and output to the DB) is connected to MET.
When I check for DC voltage to earth, what level of reading should I expect to find for a good or fault condition?
Thanks again.

0v ideally. Try and pick a wet day when you do it.

Better still, do you have an insulation resistance tester? If you do, isolate the DC side and access the terminals inside the isolator. With 12 panels your system is almost certainly single string with one DC isolator. Test between + to Earth and - Earth @500vdc and see what you get. Again, test on a wet day if you can.
 
On a damp day, had been raining before we started, removed cover from isolation switches. With a multi meter, carried out earth voltage check between DC + and earth. DC- and earth. Both readings recorded zero voltage. Unable to carry out resistance test as my resistance tester was duff.
NB. Since an earth conductor had been added between the FIT meter and the enclosure for the AC switches (via MET) no further error messages have appeared and all appears OK.
For future reference, are there any Forum members with contact details of repairers in Cheshire/Widnes area who could assist if further work is required?
 

Reply to Isolation Fault in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hello everyone, I'm newly registered having read the boards from the shadows for a while. I have a question about neutral to earth faults and...
Replies
24
Views
6K
Hi. I have a flat with a Pulsacoil Eco that is now 4 years old. I have recently had a new tenant move in and for the week in between tenancies the...
Replies
2
Views
1K
hello. just wondered if any of you have experienced this or can possibly shed some light on it. today i went to a fault on an immersion circuit...
Replies
26
Views
3K
J
Hi I am having a few issues with the earthing at my house. This is a bit long winded but hopefully you can understand. I am not a time served...
Replies
37
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top