Search for tools and product advice,

Discuss Issues with old light fitting replacement in the UK Electrical Forum area at ElectriciansForums.net

DIYdan

DIY
Reaction score
13
Hi all.

Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working before. Any idea where I'm going wrong? The old light fitting had all neutral and all live to the wrapped and inserted into the corresponding terminals and then the seperate black wire elsewhere which I'm guessing is for the switch. I'm trying to replace with a ceiling rose. Thanks
 

Attachments

  • 20240415_113042.jpg
    321.5 KB · Views: 48
  • 20240415_113049.jpg
    193.5 KB · Views: 39
Can you show how it is currently connected?
Hi, it's as shown in the pic now. I had all the live to the live and all the neutral to neutral, the singular black wire I thought at first to be earth but it wasn't, I tried placing it in the loop section but still no light switch functionality and I also tried placing it in a neutral point but that then flipped the fuse
 
The single black is the return from the switch this goes to the live of the light. Keep all the reds together but not connected to the light. The other blacks are neutral. Those bare earths tucked into the ceiling need sleeving and correctly connecting together, I suspect they are just twisted. Does the light need an earth?
What connectors are you using for all those wires?
 
The single black is the return from the switch this goes to the live of the light. Keep all the reds together but not connected to the light. The other blacks are neutral. Those bare earths tucked into the ceiling need sleeving and correctly connecting together, I suspect they are just twisted. Does the light need an earth?
What connectors are you using for all those wires?
Ahh so the single black wire goes to live. That's where I must have been going wrong then. There isn't enough space on the rose so I'll join all the reds and blacks via a wago. The earth wire were like that when I pulled the socket so doesn't seem to be needed.

So just to confirm all reds to live, all neutrals to neutral and then the single black to live aswell. I'll be back at the house shortly so will hook it all up and report back. Thanks for the assist.

I don't do a lot of stuff that causes me issues, I mostly do games console repairs, but each time I've come here it's been super quick replies and great help, so thanks very much, I appreciate you 👍
 
No the reds together but not connected to the light the only live to the light is that single black. What sort of light are you fitting because those earths and all connections require correct enclosures, not pushed into the ceiling. Maybe this should be left to a professional.
 
No the reds together but not connected to the light the only live to the light is that single black. What sort of light are you fitting because those earths and all connections require correct enclosures, not pushed into the ceiling. Maybe this should be left to a professional.
The reds were all connected together and connected into the old fitting, along with the blacks and single black wire. I'm trying to replace it with a rose fitting
 
If it was an old batten holder they would have been connected to a terminal on it this was the loop but it was just a terminal for those wires. If you are fitting a rose all those wires including the earths need connecting within it. This can be done but is possibly beyond what you can do.
 
If it was an old batten holder they would have been connected to a terminal on it this was the loop but it was just a terminal for those wires. If you are fitting a rose all those wires including the earths need connecting within it. This can be done but is possibly beyond what you can do.
Yeah the fitting was ancient. OK so using the modern rose needs the earths connecting aswell.

So all live and neutral connected.

Single black wire to loop and then connect the earths once I've shielded them.
 
I'm sorry to say that is a totally inappropriate and dangerous way to do it. Unenclosed connections in the ceiling void are a fire hazard so you created a potentially dangerous situation. Is it your house?
 
I'm sorry to say that is a totally inappropriate and dangerous way to do it. Unenclosed connections in the ceiling void are a fire hazard so you created a potentially dangerous situation. Is it your house?
The connections are enclosed within the connectors. There is no void, just a little plaster chipped away
 
OMG, a rewire is imminent lol
 

Reply to Issues with old light fitting replacement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
705
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Done a job yesterday, remove old 12v halogens and replace with mains, gu10 downlights. Fitted some LED gu10's no issues. Got a call today saying...
Replies
9
Views
886
Good Morning need some advice please. Yesterday went to change a light fitting in hallway. There are two ceiling lights in the hall controlled by...
Replies
6
Views
270

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock