That is not really the case though as even a domestic TT system can have currents to tens of amps on each final circuit, but a 200 ohm rod so PFC below 1A. I guess the defining point would be not the FLC but the operating point of the designed protection system (so in such a TT case the RCD would be tripping typically for faults below 7.6k ohm at most).
Which kind of returns to the original discussion about IT systems and that they are normally designed to continue under single fault conditions, and ideally safely (as far as practical) so you might be looking at earthing impedances of tens of k ohm if trying to keep the 2nd fault touch shock current below, say, 10mA (assuming that is even possible depending on filter caps, etc).