0
Hi,

Apologies for the basic (silly!) question, but using a maintenance free box (ashley j803) to extend a ring main circuit, in the configuration in the image attached with 4 cables (2 in, 2 out), would it not create issues having the separate 2 cables in and out, in contact with each other? Should they not be connected separately (2 junction boxes) or is everything connected to each other in the end and it doesn't matter?

Cheers!

J803.jpg
 
This would be known as a 'figure of eight' RFC, is not permitted, and there is a specific test prescribed in the regs. to root any such arrangements out.
Either 6 pole j/box, or two separate 3 pole is required.
 

Reply to Junction Box Question in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
890
Hi Everyone, Sorry in advance if this is a silly question. There is a junction box in my mother's kitchen, on the wall above her kitchen...
Replies
5
Views
956
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
890
I collect old Electrical Fittings and I recently acquired this vintage Junction Box (photos attached). I've been trying to figure out how it would...
Replies
4
Views
714
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock