Hi all,

I think I'm posting this in the right place - apologies if not. I'm wondering if I could ask for a bit of help here.

I'm renovating a house for myself to live in, and I've spoken to an electrician this week to have it fully rewired. There appears to be a problem though with my planned utility room layout.

The attached picture (top half) shows the layout I planned after reading up as much as I could on forums like this one. Although perhaps not ideal to have sockets below the sink, I understand the regulations allow it, and there's nowhere else to make the sockets accessible. I've fitted the trucking and back boxes, as the electrician told me I could save a bit by doing the general chasing out etc throughout the house.

This electrician refused to do it this way because, he insists, the regulations demand:

(1) that the socket for a washing machine or tumble dryer must have an isolating switch above the worktop, and cannot be in a cupboard because it's not accessible;
(2) the presence of a cupboard in front of the sockets changes the normal safe zone rules, such that the vertical yellow line is no longer a safe zone because the socket isn't immediately visible.

Everything I can find online, without exception, says his first point is wrong, and I can't find anything at all regarding his second point. Also, a friend's recently professionally-refitted kitchen has each appliance plugged into a socket in the cupboard next to it. But I'm in no way qualified to be certain, and when I tried questioning, he just dug his heels in.

The bottom half shows what he tells me is necessary. Each isolating switch must be above its appliance, and >300mm from the sink, and therefore the socket must be hidden behind the appliance. I don't want them there, mainly because they're completely inaccessible, partly because it would probably push the appliance out slightly.

Is this one of those grey areas? Or is one of us just plain wrong? I'd greatly appreciate any help.

utility electrics.png
 
Your man is uncomfortable with something different, which I can understand. As you've been advised (and seen) the connection to appliances can be in a cupboard as you've proposed. Perhaps he would be happier if the drop aligned with an outlet (as in 4) but then continued down to the lower level, then 90 degree turn and run horizontal to the appliance connections (as in 2).
 
if the sockets are behind the appliances, chances are they will foul the appliance. best in cupboards, using diagram #4, but isolators are not necessary as long as you can access the sockets without stripping the cupboards out.
 
These cases are a little bit about good practice, becoming a reference when it is then best to refer to how we get there. As at least two people have mentioned the key word "access". We even have 513.1 ACCESSIBILITY to help us.

I am working on a kitchen this week and next, so interested in this post. The gist of the regs is, a socket shall be arranged to facilitate its operation, inspection and maintenance. This should not be impaired by mounting it in an enclosure or a compartment.

The use of an isolator above the worktop, meets the requirement easily, anything else has to be thought about and meet 513.1. My first thought is the reg is not met if you put your isolator at the back of or behind a cupboard. Regards
 
These cases are a little bit about good practice, becoming a reference when it is then best to refer to how we get there. As at least two people have mentioned the key word "access". We even have 513.1 ACCESSIBILITY to help us.

I am working on a kitchen this week and next, so interested in this post. The gist of the regs is, a socket shall be arranged to facilitate its operation, inspection and maintenance. This should not be impaired by mounting it in an enclosure or a compartment.

The use of an isolator above the worktop, meets the requirement easily, anything else has to be thought about and meet 513.1. My first thought is the reg is not met if you put your isolator at the back of or behind a cupboard. Regards

On a new build, you might not comply with Document M, hence they use grid switched controlled sockets for appliances.

Doubt if the OP has this issue?
 
The gist of the regs is, a socket shall be arranged to facilitate its operation, inspection and maintenance. This should not be impaired by mounting it in an enclosure or a compartment.

Edit - just re read 513.1 - that's a really badly worded reg - wonder what the author(s) actually mean?
 
I'd go with your plan as well, but how you gonna convince your sparks?

How far back can you push your free standing appliance with socket & plug top in the way? You could replace the plug & socket (appliance) to flex outlet, but its a bit of a pain for cleaning or maintenance.
 
Reading 513.1, my take is that however it's mounted, it's to be accessible. It's use etc is not to be significantly impaired. If I can reach into the cupboard to 2nd fix and test the outlet in the normal way, then I don't feel I have created an outlet that offends this reg (?). At mine, the CU is in a cupboard.
 
Reading 513.1, my take is that however it's mounted, it's to be accessible. It's use etc is not to be significantly impaired. If I can reach into the cupboard to 2nd fix and test the outlet in the normal way, then I don't feel I have created an outlet that offends this reg (?). At mine, the CU is in a cupboard.

i.e. moving some tins of beans and cereal to gain access to a socket is easier than a 90 year old lady pulling out a washing machine!

I agree with you BTW
 
all he's got to do is stick one d/socket in base unit. why have two.
considering meter and half cable from the appliance .
the idea is having the socket in the base unit
1) to isolate it invent of the appliance catch fire .
 
Last edited:
And my new build, socket behind washer/dryer. Suppose its easier to build, that way, no faffing around after kitchen units put in. Took two of us to push the thing back & thread the waste pipe. Mind you, the plumber can faff around plumbing in the waste, so why can't the sparks do the same with a socket outlet :mad:
 
I put in sockets behind cupboards and the kitchen guy refused to put any cut outs in the backs to allow access. Waiting for the call when the w/mc has a fault and they call him back to unplug it. At least it can be isolated (Grid Switches - yuck).
Somehow managed to lose contact with him. Such a shame... not![/QUOT
Typically fitter
 
Always sockets in the cupboards for me too but if at all possible I'll bring the cables down the side from the rear in a little bit of trunking [or even clipped if the unit is sturdy] and mount the socket/s near the front of the base unit at a sensible height.
 
I personally would do it the way your electrician has stated. Isolator above, unswitched sockets/ outlet plates below.
Better design access for isolation. Part M has been taken into account.
Your way can be acceptable, but I would be strongly advising my way.
One thing I would do differently is I would have the unswitched socket /outlet plates in the cupboard next to appliances due to space issues with appliance.
 
I personally would do it the way your electrician has stated. Isolator above, unswitched sockets/ outlet plates below.
Better design access for isolation. Part M has been taken into account.
Your way can be acceptable, but I would be strongly advising my way.
One thing I would do differently is I would have the unswitched socket /outlet plates in the cupboard next to appliances due to space issues with appliance.


In that case wouldn't it be just as well to put the switched socket in there and save an unnecessary accessory and connection.
 
These cases are a little bit about good practice, becoming a reference when it is then best to refer to how we get there. As at least two people have mentioned the key word "access". We even have 513.1 ACCESSIBILITY to help us.

I am working on a kitchen this week and next, so interested in this post. The gist of the regs is, a socket shall be arranged to facilitate its operation, inspection and maintenance. This should not be impaired by mounting it in an enclosure or a compartment.

The use of an isolator above the worktop, meets the requirement easily, anything else has to be thought about and meet 513.1. My first thought is the reg is not met if you put your isolator at the back of or behind a cupboard. Regards
Don't agree with this view, personally it looks a lot better if the socket is hidden in the back of a cupboard. It is accessible for isolation even if someone has to move a box of weetabix to get to it.
Next we will have someone raising the issue of cutting plugs off appliances and invalidating the warranty again, pass me another beer!:)
 
Wow, lots of replies - big thank you to all for your advice. Seems all pretty much agree this electrician is wrong, apart from Paignton Pete - there had to be one ;)

Regarding access to the sockets - I'll be fitting all kitchen and utility room units myself, and I'll probably leave the back off that cupboard, or otherwise cut a hole for each socket, because my entire point is to keep them accessible.

On a new build... Doubt if the OP has this issue?
Not a new build, so no I don't have the problem of having to comply with that, thankfully. To Paignton Pete: I understand what you mean, but I'm not fussed about part M, so bearing that in mind, could I ask you something? If I was offering you this job, you'd explained all this to me, strongly recommending your way for easier access, and I still wanted it done my preferred way, would you refuse to do it?

Perhaps he would be happier if the drop aligned with an outlet (as in 4) but then continued down to the lower level, then 90 degree turn and run horizontal to the appliance connections (as in 2).
Thanks for the idea, that sounds a good compromise, I'll have to see if he'd be happy with that.

...best in cupboards, using diagram #4, but isolators are not necessary...
Did you mean diagram #2 rather than #4, or am I misunderstanding you?

all he's got to do is stick one d/socket in base unit. why have two.
Because I've read that a double socket still has max 13A rating but these 2 appliances together could go over that, and therefore it's safer to use 2 singles. Even if it's only a theoretical problem or if there's disagreement over it, erring on the safe side seemed logical.

Crimson - where's the bad spelling? :p
 
Because I've read that a double socket still has max 13A rating but these 2 appliances together could go over that, and therefore it's safer to use 2 singles. Even if it's only a theoretical problem or if there's disagreement over it, erring on the safe side seemed logical.

13A per point not 13A combined so technically 1 double will still be the same as 2 singles as there is 2 points to plug into that been said your paying so it ultimately up to you want get as your paying for it (as long as its safe and within regs which it is)
 
Wow, lots of replies - big thank you to all for your advice. Seems all pretty much agree this electrician is wrong, apart from Paignton Pete - there had to be one ;)

To Paignton Pete: I understand what you mean, but I'm not fussed about part M, so bearing that in mind, could I ask you something? If I was offering you this job, you'd explained all this to me, strongly recommending your way for easier access, and I still wanted it done my preferred way, would you refuse to do it?
At the end of he day you are the customer so I would do what you requested, yes.

And I prefer your electricians design to a point, but I do think he is wrong about not being able to do it your way.

There is a difference between what you are permitted to do and what you choose to do. Your electrician has chosen not to do it but he is permitted to do it.

Cheers pete
 
Thank you Pete, that's a huge help. All confirms he's wrong to tell me that way isn't legal.

I'd really rather not have the fuss and wasted time of having to find someone else, so if he still says no, then I'll see if he'd be happy to do it by adding his isolating switches next to the double sockets above the worktop, while keeping the appliance sockets in the cupboard (hiding the sockets is the part where I won't compromise). The safe zone thing for the cabling is just an annoyance becuse I've already run the trunking, but not worth fussing over, I can easily run more.

Big thanks again to everyone on this thread.
 

Reply to Kitchen appliance sockets and safe zones - right or wrong? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
927
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
942
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock