Discuss L-N Reverse and 240v on gas pipe in the UK Electrical Forum area at ElectriciansForums.net

Youve misunderstood my question, I asked where the 240V on the gas pipe was measured from, not what type of tester did you use. Is it 240V between the gas pipe and the live, the neutral, the earth, something else?

What is the fault on the RFC? As far as I can tell from your posts you haven't yet found a fault on the RFC? Plugging in a socket tester is not a valid test for identifying a type of fault, it is a rough estimate. Those things will show up a L-N reverse for other faults than just reversed polarity.
240 to earth. Used my MFT for that.
Using my voltage indicator I’m getting 230 N-E and ZeroV L-E.
 
240 to earth. Used my MFT for that.
Using my voltage indicator I’m getting 230 N-E and ZeroV L-E.

do you mean 240V to earth as in the actual physical surface of the ground? I assume you don't mean to the electrical earth as the gas is bonded so should be at the same potential as the electrical earth.

Where did you measure these 230V measurements? Are they appearing in different parts of the installation or just in one place?
 
Hi TheCodboy. I know you've checked the incoming polarity. Have you checked the polarity at the mcbs? Is it possible there has been a crossover somehow within the consumer unit? I saw a schnieder consumer unit recently where it looked quite easy to get things the wrong way around.
 
Hi all, been called out to a job today where the customer says they are getting a tingle from the gas meter and some appliances. Its a TT system, got a ze of 48 ohms. Gas bonding is 10mm and is continuous. Dual rcd board with 3 RFC's on one side of the board. There's a L-N reverse when i go around and check the sockets with my plug in, also voltage on the gas pipe. I've narrowed it down to one ring, that when i turn off, the L-N fault on the other rings goes and the voltage goes from the gas pipe. Now, ive been around the faulty RFC and checked the sockets and they are all wired up correctly. I've got end to end readings on L,N & E. When I've done a figure 8 with L-E and went around the sockets, i have as expected R1+R2 readings and >999 when i switch the socket (as you would normally expect). Connect one leg into the board and I have L-E 0v N-E 230v and L-N 230v, same when i connect the other leg.With the faulty ring connected back in, we have 240 on the gas again. Reverse polarity somewhere. The guy reckons there cant be any JB's as he pulled the cables in himself. They had some plastering work done recently but I've checked those sockets and they are wired correctly. The RCD for that side of the board is also duff, cant get it to trip. Ordered a new rcd which I'll fit tomorrow, but still doesnt solve my L-N reverse problem! Any pointers folks??
What do you mean > 999 ohms is that an IR reading?
 
Are you testing at the sockets using a plug adaptor for your MFT? If so try taking your readings from the terminations on the back, this will also help identify any loose terminations, incorrect polarity etc.

Could be an accessory screw has nicked a line when an accessory is fitted and this is causing the voltage to rise on the gas pipe as it has a better Ra than the electrode.
 
Polarity reversal means two wires swapped over. They can't swap and unswap themselves on one circuit as you connect and disconnect another, therefore polarity reversal is probably a red herring inspired by the fairy lights on the tester. Line and neutral are probably fine, but some or all of the CPC is floating about. When the tester sees a hugher voltage CPC->N than CPC->L, it suggests reverse polarity because that's one of a number of possible interpretations, but it's not the only one.

I think you need to ignore all that and take some careful continuity measurements of various earthy things. Rod, MET, CPCs, extraneous services.... what is and isn't solidly connected. It's no good saying there's 230V 'to earth' if there are multiple unconnected versions of 'earth' at different potentials.
 
462B0CFC-44B5-4B77-82CD-0FAAAB4FCD3B.jpeg
Found it. 0.00 IR L-E
 

Reply to L-N Reverse and 240v on gas pipe in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
500
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
412
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
296
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock