Discuss Large Cable Size Help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Why can't you run AWA that far? For that long a run you'd probably require single point bonding of the armour though.
if this is for flood lighting, I'd refer to the manufacturer for lamp start up data. You could end up in a world of litigation of you underside the cable and lamps drop out when the volts drop!
 
You can run AWA but you must run them in trefoil +1 or quadfoil. One end only to be earthed otherwise you will run in to major problems. Therefore a CPC is needed. The mechanical protection needed for AWA is greater. The possibility of sheath damage could render the armouring useless due to corrosion.

You’re best bet is parallel SWA's.
 
The first thing you need to determine/decide on, is what loading your going to design this installation for. To me it's pointless to run a cable or cables for 280A, when and if there is more than a good possibility of that load being upgraded to up to 400A in the not too distant future. 400A OCPD's in the way of MCCB's, these can be purchased with adjustable Ir etc, parameters that will cover easily 280A to 400A.
 

Reply to Large Cable Size Help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
524
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
562
Hi chaps. I have a potential install which is a 56kW micro array. The supply is three phase, but the array is going to be 380M from the house (yes...
Replies
12
Views
2K
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock