I was asked to look at a job locally where the bloke had 8 x 50 watt gu10 downlights in a kitchen on a 400 watt dimmer switch. He said the dimmer had stopped working but he was having to change lamps quite frequently. I said that the dimmer was on its max load and he would be better down rating the lamps to 35 watt to help it out, and I stripped circuit and tested continuity through circuit as he wanted to know the circuit wasn't causing his lamps to go via any high resistance joints. Having replaced the dimmer with an equivalent from a reputable online lighting company and changed the lamps for 35 watt ,within two weeks two lamps have gone and the dimmer has stopped working! Would a leading edge dimmer be a solution to this problem or trailing edge, I havn't really any experience with the technicalities of dimmers so any advice appreciated?
 
you need a 700watt dimmer for that lot. always take the load and x 1.8. for halogens ans dimmers.
 
I read that when gu10 lamps blow they can cause a short circuit enough to blow the dimmer? Would a trailing edge or leading edge dimmer be protected from this?
 
solution is to fit a 700 watt dimmer with an in line 3A fuse. probably need a deeper back box. you might get away with a 500w, if the halogens are 35w, but then customer will fit 50's anyway when replacing.
 
Trailing edge puts less stress on the lamps as the current is always triggered at the 0v crossing point of each cycle. A fuse in the switch will never be fast enough to protect the dimmer in a short circuit situation. The dimmers get stressed because the cold resistance of TH filament is very low and they therefore have a high switch on surge. Modern dimmers are supposed to be able to cope with this. You could try taking out the triac and replacing it with one of a higher current but similar trigger ratings.
 

Reply to leading edge dimmers? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is it possible for a single dimmer switch to control two circuits, one which dims and the other which is a discrete on/off? I would like to be...
Replies
8
Views
1K
I have carried out home wiring for 60 years as a competent person, for the last 20 years, I employ a local electrician to check my work and sign...
Replies
10
Views
1K
Hello everyone. Thank you in advance for any help you can provide. I tried installing a dimmer to a 3-way circuit. The dimmer has a hard...
Replies
3
Views
1K
I successfully installed one new dimmer switch today, but ran into an issue with the second. There are two one-way switches: one switch operates...
Replies
0
Views
614
Hey folks Apologies if my question is too basic. I am an Electrical Engineer but do not work in the field. I am looking for feedback to ensure...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top